531.3.2 (ii)
It does say 'considered'.
The same reg also mentions split RCD though so i don't think it means RCBO's are required in residential premises.
'Regulation 531.3.5.3.2.201 requires that where Class I enclosures are installed in installations forming part of a TT system and RCD protection is used on outgoing circuits, all live conductors on the supply side of the incoming device must have double or reinforced insulation'.
Taken from NICEIC website.
For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double
or reinforced insulation of all live conductors (incoming cables, extension terminals, etc.) on the supply side of the
incoming device, e.g. main switch, shall be used. Insulated and non-metallic sheathed cables are deemed to meet the
requirements of double or reinforced insulation.
NOTE 1: When selecting equipment, consideration should be given to the assembly manufacturer's internal line interconnecting
cable links on the supply side of an RCD being insulated and non-metallic sheathed, or having reinforced insulation
or equivalent mechanical protection.
From the book.
Supply side of eg main switch is massively ambiguous imo.
From the book.
You were asking about the main tails and argued that :-
Only as it pertains to a pre-assembled board's link cables as far as i can see.
I was merely pointing out that it does mention DI tails or reinforced insulation.
That quote though says that all individual circuits must have their own DP isolating device. Yet the regs don't mention it.
If that were the case would it mean that all the 1000s of consumer units that use mcbs are not compliant ?
From the book.
It doesn't say required it suggests them.
Nah i'm on about the load side of the main switch to the supply of the RCD's which is what the picture in OSG shows.
'Other than at the origin of the installation, every circuit...that may have to be isolated without interrupting the supply to other circuits should be provided with its own isolating device. The device must switch all live conductors in a TT system and all line conductors in a TN system.'
This basically says all breakers have to be double pole in a TT, no?
Yet you go to 132.15.201 which the OSG references and it says absolutely nothing about this.
The DP main switch makes it compliant.
I don't believe these two statements can be reconciled.
swaRRR
Deleted account
England
Why is split RCD not appropriate for TT?
Thread Tags
swaRRR,
Tart83,