#32 shows the amended Reg see the blue book to compare.More than somewhat confused!
Has there just been a change in the relevant regs, or is the argument that we have been applying them incorrectly all along?
Whos we ? lolMore than somewhat confused!
Has there just been a change in the relevant regs, or is the argument that we have been applying them incorrectly all along?
That is the way I see it.Yet another debate caused by ambiguous wording in the book.
I think I may have changed my mind on this, and take it that the supplies to other buildings bit only applies to TN-S, not PME.
Err.....I think!
Whos we ? lol
But both 544.1.1 and 54.8 have the caveat "except where PME conditions apply"For pme it's not the c.s.a. of the meter tails that is used for Table 54.8, but the c.s.a. of the PEN conductor in the supply cable to the service head
For a supply on a standard cutout of 100A or less, the supply conductor will be 35mm or smaller. As such, the sizes for the earth conductor to the MET and onwards to the CU will be 16mm for a PME supply, and 10mm from the MET to where the gas / water enter (assuming the water is metallic). For a supply greater than 100A you should be asking the DNO
I'm confused - in blue book you are referred to 54.8 specifically "where PME conditions apply"But both 544.1.1 and 54.8 have the caveat "except where PME conditions apply"
Page 48 of the on-site guide simplifies thingsBut both 544.1.1 and 54.8 have the caveat "except where PME conditions apply"
That is the crux of the matter.
I take it to mean if the conductors are part of the PME system (i.e. the combined part) then table 54.8 and 10mm^2 or 6mm^2 etc do not apply, and no figures are specified within the wiring regs.
In all other cases - where the conductors have been separated (after the service head) then the conditions in table 54.8 and 544.1.1 are applicable.
If it did just simply mean "except for PME" then that would be the wording.
Why write the clause as particular to PME conditions, if they didn't mean where it is part of the PME (TN-C ) aspect.
Taking "except where PME conditions apply" to mean you can't use that table or regulation when dealing with part of the PME system fits the words, and the fact that the bonding size isn't specified.
Taking "except where PME conditions apply" to mean that the bonding size in the regulation and table isn't applicable to an installation supplied by a PME system begs the questions 1) what cable size should be used as 54.8 is "except where PME conditions apply" so what size for PME; and 2) why the "odd" wording, why not just say 'except for installations supplied from PME"?
The heading for table 54.8 says 'minimum csa of the main protective bonding conductor in relation to the PEN conductor of the supply' so surely that is the csa of the DNO supply cable combined neutral earth, which as was mentioned previously in a domestic supply would be 35mm or less?I am confused also!
The heading for table 54.8 says 'minimum csa of the main protective bonding conductor in relation to the PEN conductor of the supply' so surely that is the csa of the DNO supply cable combined neutral earth, which as was mentioned previously in a domestic supply would be 35mm or less?
So in @cliffed s case above I would have thought 10mm or equivalent in steel, the combined swa of the cable and cpc would be sufficient to cover that? But then what is the supply connected to wasn't it an existing ring final, in which case the earthing conductor from there would only be 3mm and as such undersize?
My brain hurts!
Ps @mainline I think pages 55 and 56 osg do a better job.
I don't think this is new ?I think this is wandering slightly, from early on in the thread the interpretation of the new Regulation 544.1.1 is what is being brought into question.
It isn't a new Regulation it has been reworked so you need to compare both you will then understand the core debate here.I don't think this is new ?
Damn, I missed a chunk.It isn't a new Regulation it has been reworked so you need to compare both you will then understand the core debate here.