Client wants 2g socket in greenhouse, obviously IP rated,will be supplied from Rcd, the greenhouse consists of metal frame work on the ground.
Does this require MPBC
 
So if you believe that the PME note means that in any case where a PME is used to supply a property, the values in 54.8 and 544.1.1 are not correct , just where do you get the correct size from?

Wouldn't this be a glaring omission from the regs? - inability to size bonding if it's supplied via PME.


Or should we understand that "where PME conditions apply" refers to those situations where the Neutral and earth are combined (CNE) forming part of the PME configuration.

In which case, once they have been split at the service head then 54.8 and 544.1.1 apply in terms if bonding size.
The way I view that Regulation is that if you have an installation where the source of supply is PME then it cannot be applied. If I have remote building from such a supply and the requirements for main protective bonding is 25.0 then this applies throughout and as such any distribution cable must be able to support it.
 
The way I view that Regulation is that if you have an installation where the source of supply is PME then it cannot be applied. If I have remote building from such a supply and the requirements for main protective bonding is 25.0 then this applies throughout and as such any distribution cable must be able to support it.
Agree that’s my interpretation of the requirement
 
The way I view that Regulation is that if you have an installation where the source of supply is PME then it cannot be applied. If I have remote building from such a supply and the requirements for main protective bonding is 25.0 then this applies throughout and as such any distribution cable must be able to support it.
If "except where PME conditions apply " means the same as 'except where the supply to the installation is PME"

then where is the size of bonding conductor defined within the regs?

It would appear to be totally wrong if the regs don't actually provide details for bonding size in the most common type of earthing arrangement used, yet do provide suitable guidance/rules for the less common versions.

For years most have used10mm^2, but if you do apply the "except where PME conditions apply " to mean 'except where the supply to the installation is PME" then there would be no justification for that, or any other size as both 54.1.1 and 54.8 both include the note that they do not apply where PME conditions apply.

Even using 25mm^2 wouldn't have any justification, especially as the temperature rise of CNE cable provides different loading compared to single core, hence DNOs have different cable ratings.
 
I shall be installing a TT System with the appropriate MPBC
If "except where PME conditions apply " means the same as 'except where the supply to the installation is PME"

then where is the size of bonding conductor defined within the regs?

It would appear to be totally wrong if the regs don't actually provide details for bonding size in the most common type of earthing arrangement used, yet do provide suitable guidance/rules for the less common versions.

For years most have used10mm^2, but if you do apply the "except where PME conditions apply " to mean 'except where the supply to the installation is PME" then there would be no justification for that, or any other size as both 54.1.1 and 54.8 both include the note that they do not apply where PME conditions apply.

Even using 25mm^2 wouldn't have any justification, especially as the temperature rise of CNE cable provides different loading compared to single core, hence DNOs have different cable ratings.
If the main supply type is a TNC-S (PME), then selection of main protective bonding conductor sizes is completed by reference to table 54.5 of BS7671.

To summarise this table, sizing is completed by reference to the size of the PEN (Protective Earth Neutral) conductor of the supply. PEN conductors of anything less than 35mm2 require a minimum of 10mm2 bonding conductors. PEN conductors between 35mm2 & 50mm2 require a 16mm2 bonding conductor to be used. The sizes of the required bonding conductors increase significantly as the size of the PEN conductor rises.

PME main bonding conductors are not subject the 25mm2 maximum requirement of any other supply type. The largest required bonding conductors on any PME supply is with an incoming supply PEN conductor of more than 150mm2 which requires a considerable 50mm2 bonding conductor to be installed!
 
If the main supply type is a TNC-S (PME), then selection of main protective bonding conductor sizes is completed by reference to table 54.5 of BS7671.

To summarise this table, sizing is completed by reference to the size of the PEN (Protective Earth Neutral) conductor of the supply. PEN conductors of anything less than 35mm2 require a minimum of 10mm2 bonding conductors. PEN conductors between 35mm2 & 50mm2 require a 16mm2 bonding conductor to be used. The sizes of the required bonding conductors increase significantly as the size of the PEN conductor rises.

PME main bonding conductors are not subject the 25mm2 maximum requirement of any other supply type. The largest required bonding conductors on any PME supply is with an incoming supply PEN conductor of more than 150mm2 which requires a considerable 50mm2 bonding conductor to be installed!
That's exactly my point, if this table applies to PME (and other TN arrangements) then it does mean that "except where PME conditions apply " doesn't mean that just because the supply is PME that this exception applies.

To me it's simple

If the "except where PME conditions apply " means the same as 'except where the supply to the installation is PME" then there is no sizing provided for installations supplied via PME within the wiring regs. (Which doesn't make sense.)

On the other hand if "except where PME conditions apply " means exactly that, then you would use table 54.8/544.1.1 in their entirely for all TN supplies including PME.

If you were to deal with a "where PME conditions apply" situation, such as street furniture etc. direct from the utility supply, (i.e. before the CNE is split in the service head) then you would need to obtain that sizing from the utility - which is typically 35mm^2 for most applications, but perhaps 16mm^2 for street lighting and consumer services.

This latter aspect is not contained within the wiring regs.
 
That's exactly my point, if this table applies to PME (and other TN arrangements) then it does mean that "except where PME conditions apply " doesn't mean that just because the supply is PME that this exception applies.

To me it's simple

If the "except where PME conditions apply " means the same as 'except where the supply to the installation is PME" then there is no sizing provided for installations supplied via PME within the wiring regs. (Which doesn't make sense.)

On the other hand if "except where PME conditions apply " means exactly that, then you would use table 54.8/544.1.1 in their entirely for all TN supplies including PME.

If you were to deal with a "where PME conditions apply" situation, such as street furniture etc. direct from the utility supply, (i.e. before the CNE is split in the service head) then you would need to obtain that sizing from the utility - which is typically 35mm^2 for most applications, but perhaps 16mm^2 for street lighting and consumer services.

This latter aspect is not contained within the wiring regs.
Sorry I am not reading the way you are.
 
Yet another debate caused by ambiguous wording in the book.
I think I may have changed my mind on this, and take it that the supplies to other buildings bit only applies to TN-S, not PME.
Err.....I think!
 
That's exactly my point, if this table applies to PME (and other TN arrangements) then it does mean that "except where PME conditions apply " doesn't mean that just because the supply is PME that this exception applies.

To me it's simple

If the "except where PME conditions apply " means the same as 'except where the supply to the installation is PME" then there is no sizing provided for installations supplied via PME within the wiring regs. (Which doesn't make sense.)

On the other hand if "except where PME conditions apply " means exactly that, then you would use table 54.8/544.1.1 in their entirely for all TN supplies including PME.

If you were to deal with a "where PME conditions apply" situation, such as street furniture etc. direct from the utility supply, (i.e. before the CNE is split in the service head) then you would need to obtain that sizing from the utility - which is typically 35mm^2 for most applications, but perhaps 16mm^2 for street lighting and consumer services.

This latter aspect is not contained within the wiring regs.
For pme it's not the c.s.a. of the meter tails that is used for Table 54.8, but the c.s.a. of the PEN conductor in the supply cable to the service head
For a supply on a standard cutout of 100A or less, the supply conductor will be 35mm or smaller. As such, the sizes for the earth conductor to the MET and onwards to the CU will be 16mm for a PME supply, and 10mm from the MET to where the gas / water enter (assuming the water is metallic). For a supply greater than 100A you should be asking the DNO
 
Yet another debate caused by ambiguous wording in the book.
I think I may have changed my mind on this, and take it that the supplies to other buildings bit only applies to TN-S, not PME.
Err.....I think!
Which is why suppliers frown on exporting pme
 
This has become somewhat confused I asked in #22 if this applied to all TN systems and whilst TN-C-S does not necessarily mean PME I was answered yes it does but it doesn't?
More than somewhat confused!
Has there just been a change in the relevant regs, or is the argument that we have been applying them incorrectly all along?
 
Yet another debate caused by ambiguous wording in the book.
I think I may have changed my mind on this, and take it that the supplies to other buildings bit only applies to TN-S, not PME.
Err.....I think!
That is the way I see it.
 

Attachments

  • [ElectriciansForums.net] Power point in external glasshouse
    55.jpg
    44 KB · Views: 35
For pme it's not the c.s.a. of the meter tails that is used for Table 54.8, but the c.s.a. of the PEN conductor in the supply cable to the service head
For a supply on a standard cutout of 100A or less, the supply conductor will be 35mm or smaller. As such, the sizes for the earth conductor to the MET and onwards to the CU will be 16mm for a PME supply, and 10mm from the MET to where the gas / water enter (assuming the water is metallic). For a supply greater than 100A you should be asking the DNO
But both 544.1.1 and 54.8 have the caveat "except where PME conditions apply"

That is the crux of the matter.

I take it to mean if the conductors are part of the PME system (i.e. the combined part) then table 54.8 and 10mm^2 or 6mm^2 etc do not apply, and no figures are specified within the wiring regs.

In all other cases - where the conductors have been separated (after the service head) then the conditions in table 54.8 and 544.1.1 are applicable.

If it did just simply mean "except for PME" then that would be the wording.

Why write the clause as particular to PME conditions, if they didn't mean where it is part of the PME (TN-C ) aspect.

Taking "except where PME conditions apply" to mean you can't use that table or regulation when dealing with part of the PME system fits the words, and the fact that the bonding size isn't specified.

Taking "except where PME conditions apply" to mean that the bonding size in the regulation and table isn't applicable to an installation supplied by a PME system begs the questions 1) what cable size should be used as 54.8 is "except where PME conditions apply" so what size for PME; and 2) why the "odd" wording, why not just say 'except for installations supplied from PME"?
 
I'm at a disadvantage here, as I'm hanging out for a breakfast roll which comes with a free Amendment 2 book, and so don't have the new book yet.
Trying to summarise, for my own benefit, and because this is getting highly confusing, and first looking at the blue book, we have:
-a paragraph about NOT PME, saying main bonding should be 50% of earthing conductor and bigger that 6mm
-a sentence about PME (except highway / street stuff), saying look at 54.8
-a sentence about more that one source of supply.

From the scan above, the new book has exactly the same structure, with one extra bit tacked onto the end of the first point.
The extra bit adds a bit more leeway for the size of bonding in submains.

Am I understanding correctly that the complex debate is whether the new bit applies to all installations, or only 'NOT PME' installations?
But both 544.1.1 and 54.8 have the caveat "except where PME conditions apply"
I'm confused - in blue book you are referred to 54.8 specifically "where PME conditions apply"
I'm not seeing the caveat for 54.8 in blue book or in the scan above - can you help me out?
 
PME conditions is the nature of your supply and the condition is the earthing and main protective bonding requirements satisfy these conditions hence that Regulation does not apply.
 
But both 544.1.1 and 54.8 have the caveat "except where PME conditions apply"

That is the crux of the matter.

I take it to mean if the conductors are part of the PME system (i.e. the combined part) then table 54.8 and 10mm^2 or 6mm^2 etc do not apply, and no figures are specified within the wiring regs.

In all other cases - where the conductors have been separated (after the service head) then the conditions in table 54.8 and 544.1.1 are applicable.

If it did just simply mean "except for PME" then that would be the wording.

Why write the clause as particular to PME conditions, if they didn't mean where it is part of the PME (TN-C ) aspect.

Taking "except where PME conditions apply" to mean you can't use that table or regulation when dealing with part of the PME system fits the words, and the fact that the bonding size isn't specified.

Taking "except where PME conditions apply" to mean that the bonding size in the regulation and table isn't applicable to an installation supplied by a PME system begs the questions 1) what cable size should be used as 54.8 is "except where PME conditions apply" so what size for PME; and 2) why the "odd" wording, why not just say 'except for installations supplied from PME"?
Page 48 of the on-site guide simplifies things
 
I am confused also!
The heading for table 54.8 says 'minimum csa of the main protective bonding conductor in relation to the PEN conductor of the supply' so surely that is the csa of the DNO supply cable combined neutral earth, which as was mentioned previously in a domestic supply would be 35mm or less?
So in @cliffed s case above I would have thought 10mm or equivalent in steel, the combined swa of the cable and cpc would be sufficient to cover that? But then what is the supply connected to wasn't it an existing ring final, in which case the earthing conductor from there would only be 3mm and as such undersize?
My brain hurts!

Ps @mainline I think pages 55 and 56 osg do a better job.
🙂
 
I am confused also!
The heading for table 54.8 says 'minimum csa of the main protective bonding conductor in relation to the PEN conductor of the supply' so surely that is the csa of the DNO supply cable combined neutral earth, which as was mentioned previously in a domestic supply would be 35mm or less?
So in @cliffed s case above I would have thought 10mm or equivalent in steel, the combined swa of the cable and cpc would be sufficient to cover that? But then what is the supply connected to wasn't it an existing ring final, in which case the earthing conductor from there would only be 3mm and as such undersize?
My brain hurts!

Ps @mainline I think pages 55 and 56 osg do a better job.
🙂
The heading for table 54.8 says 'minimum csa of the main protective bonding conductor in relation to the PEN conductor of the supply' so surely that is the csa of the DNO supply cable combined neutral earth, which as was mentioned previously in a domestic supply would be 35mm or less?

Correct

So in @cliffed s case above I would have thought 10mm or equivalent in steel, the combined swa of the cable and cpc would be sufficient to cover that?

It may very well do

But then what is the supply connected to wasn't it an existing ring final, in which case the earthing conductor from there would only be 3mm and as such undersize?

His problem is using the cpc as bonding to the greenhouse.


Page 55 blue osg is switching and page 56 is blank
 
Last edited:

Reply to Power point in external glasshouse in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Personally, I would take a Ze measurement myself rather than rely on someone else's maybe drive by scrap of paper.
2
Replies
31
Views
2K
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
404
Good Afternoon All, So I have a new situation to me that I cannot seem to get a definitive answer for. I trained as an electrician and did...
Replies
0
Views
1K
  • Question
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...
Replies
4
Views
1K
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks