Client wants 2g socket in greenhouse, obviously IP rated,will be supplied from Rcd, the greenhouse consists of metal frame work on the ground.
Does this require MPBC
 
Yet another debate caused by ambiguous wording in the book.
I think I may have changed my mind on this, and take it that the supplies to other buildings bit only applies to TN-S, not PME.
Err.....I think!
That is the way I see it.
 

Attachments

  • [ElectriciansForums.net] Power point in external glasshouse
    55.jpg
    44 KB · Views: 37
For pme it's not the c.s.a. of the meter tails that is used for Table 54.8, but the c.s.a. of the PEN conductor in the supply cable to the service head
For a supply on a standard cutout of 100A or less, the supply conductor will be 35mm or smaller. As such, the sizes for the earth conductor to the MET and onwards to the CU will be 16mm for a PME supply, and 10mm from the MET to where the gas / water enter (assuming the water is metallic). For a supply greater than 100A you should be asking the DNO
But both 544.1.1 and 54.8 have the caveat "except where PME conditions apply"

That is the crux of the matter.

I take it to mean if the conductors are part of the PME system (i.e. the combined part) then table 54.8 and 10mm^2 or 6mm^2 etc do not apply, and no figures are specified within the wiring regs.

In all other cases - where the conductors have been separated (after the service head) then the conditions in table 54.8 and 544.1.1 are applicable.

If it did just simply mean "except for PME" then that would be the wording.

Why write the clause as particular to PME conditions, if they didn't mean where it is part of the PME (TN-C ) aspect.

Taking "except where PME conditions apply" to mean you can't use that table or regulation when dealing with part of the PME system fits the words, and the fact that the bonding size isn't specified.

Taking "except where PME conditions apply" to mean that the bonding size in the regulation and table isn't applicable to an installation supplied by a PME system begs the questions 1) what cable size should be used as 54.8 is "except where PME conditions apply" so what size for PME; and 2) why the "odd" wording, why not just say 'except for installations supplied from PME"?
 
I'm at a disadvantage here, as I'm hanging out for a breakfast roll which comes with a free Amendment 2 book, and so don't have the new book yet.
Trying to summarise, for my own benefit, and because this is getting highly confusing, and first looking at the blue book, we have:
-a paragraph about NOT PME, saying main bonding should be 50% of earthing conductor and bigger that 6mm
-a sentence about PME (except highway / street stuff), saying look at 54.8
-a sentence about more that one source of supply.

From the scan above, the new book has exactly the same structure, with one extra bit tacked onto the end of the first point.
The extra bit adds a bit more leeway for the size of bonding in submains.

Am I understanding correctly that the complex debate is whether the new bit applies to all installations, or only 'NOT PME' installations?
But both 544.1.1 and 54.8 have the caveat "except where PME conditions apply"
I'm confused - in blue book you are referred to 54.8 specifically "where PME conditions apply"
I'm not seeing the caveat for 54.8 in blue book or in the scan above - can you help me out?
 
PME conditions is the nature of your supply and the condition is the earthing and main protective bonding requirements satisfy these conditions hence that Regulation does not apply.
 
But both 544.1.1 and 54.8 have the caveat "except where PME conditions apply"

That is the crux of the matter.

I take it to mean if the conductors are part of the PME system (i.e. the combined part) then table 54.8 and 10mm^2 or 6mm^2 etc do not apply, and no figures are specified within the wiring regs.

In all other cases - where the conductors have been separated (after the service head) then the conditions in table 54.8 and 544.1.1 are applicable.

If it did just simply mean "except for PME" then that would be the wording.

Why write the clause as particular to PME conditions, if they didn't mean where it is part of the PME (TN-C ) aspect.

Taking "except where PME conditions apply" to mean you can't use that table or regulation when dealing with part of the PME system fits the words, and the fact that the bonding size isn't specified.

Taking "except where PME conditions apply" to mean that the bonding size in the regulation and table isn't applicable to an installation supplied by a PME system begs the questions 1) what cable size should be used as 54.8 is "except where PME conditions apply" so what size for PME; and 2) why the "odd" wording, why not just say 'except for installations supplied from PME"?
Page 48 of the on-site guide simplifies things
 
I am confused also!
The heading for table 54.8 says 'minimum csa of the main protective bonding conductor in relation to the PEN conductor of the supply' so surely that is the csa of the DNO supply cable combined neutral earth, which as was mentioned previously in a domestic supply would be 35mm or less?
So in @cliffed s case above I would have thought 10mm or equivalent in steel, the combined swa of the cable and cpc would be sufficient to cover that? But then what is the supply connected to wasn't it an existing ring final, in which case the earthing conductor from there would only be 3mm and as such undersize?
My brain hurts!

Ps @mainline I think pages 55 and 56 osg do a better job.
🙂
 
I am confused also!
The heading for table 54.8 says 'minimum csa of the main protective bonding conductor in relation to the PEN conductor of the supply' so surely that is the csa of the DNO supply cable combined neutral earth, which as was mentioned previously in a domestic supply would be 35mm or less?
So in @cliffed s case above I would have thought 10mm or equivalent in steel, the combined swa of the cable and cpc would be sufficient to cover that? But then what is the supply connected to wasn't it an existing ring final, in which case the earthing conductor from there would only be 3mm and as such undersize?
My brain hurts!

Ps @mainline I think pages 55 and 56 osg do a better job.
🙂
The heading for table 54.8 says 'minimum csa of the main protective bonding conductor in relation to the PEN conductor of the supply' so surely that is the csa of the DNO supply cable combined neutral earth, which as was mentioned previously in a domestic supply would be 35mm or less?

Correct

So in @cliffed s case above I would have thought 10mm or equivalent in steel, the combined swa of the cable and cpc would be sufficient to cover that?

It may very well do

But then what is the supply connected to wasn't it an existing ring final, in which case the earthing conductor from there would only be 3mm and as such undersize?

His problem is using the cpc as bonding to the greenhouse.


Page 55 blue osg is switching and page 56 is blank
 
Last edited:

Reply to Power point in external glasshouse in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
353
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
320
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
368

Similar threads

  • Question
Personally, I would take a Ze measurement myself rather than rely on someone else's maybe drive by scrap of paper.
2 3
Replies
31
Views
2K
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
606

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top