The way I view that Regulation is that if you have an installation where the source of supply is PME then it cannot be applied. If I have remote building from such a supply and the requirements for main protective bonding is 25.0 then this applies throughout and as such any distribution cable must be able to support it.So if you believe that the PME note means that in any case where a PME is used to supply a property, the values in 54.8 and 544.1.1 are not correct , just where do you get the correct size from?
Wouldn't this be a glaring omission from the regs? - inability to size bonding if it's supplied via PME.
Or should we understand that "where PME conditions apply" refers to those situations where the Neutral and earth are combined (CNE) forming part of the PME configuration.
In which case, once they have been split at the service head then 54.8 and 544.1.1 apply in terms if bonding size.
Agree that’s my interpretation of the requirementThe way I view that Regulation is that if you have an installation where the source of supply is PME then it cannot be applied. If I have remote building from such a supply and the requirements for main protective bonding is 25.0 then this applies throughout and as such any distribution cable must be able to support it.
If "except where PME conditions apply " means the same as 'except where the supply to the installation is PME"The way I view that Regulation is that if you have an installation where the source of supply is PME then it cannot be applied. If I have remote building from such a supply and the requirements for main protective bonding is 25.0 then this applies throughout and as such any distribution cable must be able to support it.
I shall be installing a TT System with the appropriate MPBC
If the main supply type is a TNC-S (PME), then selection of main protective bonding conductor sizes is completed by reference to table 54.5 of BS7671.If "except where PME conditions apply " means the same as 'except where the supply to the installation is PME"
then where is the size of bonding conductor defined within the regs?
It would appear to be totally wrong if the regs don't actually provide details for bonding size in the most common type of earthing arrangement used, yet do provide suitable guidance/rules for the less common versions.
For years most have used10mm^2, but if you do apply the "except where PME conditions apply " to mean 'except where the supply to the installation is PME" then there would be no justification for that, or any other size as both 54.1.1 and 54.8 both include the note that they do not apply where PME conditions apply.
Even using 25mm^2 wouldn't have any justification, especially as the temperature rise of CNE cable provides different loading compared to single core, hence DNOs have different cable ratings.
That's exactly my point, if this table applies to PME (and other TN arrangements) then it does mean that "except where PME conditions apply " doesn't mean that just because the supply is PME that this exception applies.If the main supply type is a TNC-S (PME), then selection of main protective bonding conductor sizes is completed by reference to table 54.5 of BS7671.
To summarise this table, sizing is completed by reference to the size of the PEN (Protective Earth Neutral) conductor of the supply. PEN conductors of anything less than 35mm2 require a minimum of 10mm2 bonding conductors. PEN conductors between 35mm2 & 50mm2 require a 16mm2 bonding conductor to be used. The sizes of the required bonding conductors increase significantly as the size of the PEN conductor rises.
PME main bonding conductors are not subject the 25mm2 maximum requirement of any other supply type. The largest required bonding conductors on any PME supply is with an incoming supply PEN conductor of more than 150mm2 which requires a considerable 50mm2 bonding conductor to be installed!
Sorry I am not reading the way you are.That's exactly my point, if this table applies to PME (and other TN arrangements) then it does mean that "except where PME conditions apply " doesn't mean that just because the supply is PME that this exception applies.
To me it's simple
If the "except where PME conditions apply " means the same as 'except where the supply to the installation is PME" then there is no sizing provided for installations supplied via PME within the wiring regs. (Which doesn't make sense.)
On the other hand if "except where PME conditions apply " means exactly that, then you would use table 54.8/544.1.1 in their entirely for all TN supplies including PME.
If you were to deal with a "where PME conditions apply" situation, such as street furniture etc. direct from the utility supply, (i.e. before the CNE is split in the service head) then you would need to obtain that sizing from the utility - which is typically 35mm^2 for most applications, but perhaps 16mm^2 for street lighting and consumer services.
This latter aspect is not contained within the wiring regs.
For pme it's not the c.s.a. of the meter tails that is used for Table 54.8, but the c.s.a. of the PEN conductor in the supply cable to the service headThat's exactly my point, if this table applies to PME (and other TN arrangements) then it does mean that "except where PME conditions apply " doesn't mean that just because the supply is PME that this exception applies.
To me it's simple
If the "except where PME conditions apply " means the same as 'except where the supply to the installation is PME" then there is no sizing provided for installations supplied via PME within the wiring regs. (Which doesn't make sense.)
On the other hand if "except where PME conditions apply " means exactly that, then you would use table 54.8/544.1.1 in their entirely for all TN supplies including PME.
If you were to deal with a "where PME conditions apply" situation, such as street furniture etc. direct from the utility supply, (i.e. before the CNE is split in the service head) then you would need to obtain that sizing from the utility - which is typically 35mm^2 for most applications, but perhaps 16mm^2 for street lighting and consumer services.
This latter aspect is not contained within the wiring regs.
Which is why suppliers frown on exporting pmeYet another debate caused by ambiguous wording in the book.
I think I may have changed my mind on this, and take it that the supplies to other buildings bit only applies to TN-S, not PME.
Err.....I think!
More than somewhat confused!This has become somewhat confused I asked in #22 if this applied to all TN systems and whilst TN-C-S does not necessarily mean PME I was answered yes it does but it doesn't?
#32 shows the amended Reg see the blue book to compare.More than somewhat confused!
Has there just been a change in the relevant regs, or is the argument that we have been applying them incorrectly all along?
Whos we ? lolMore than somewhat confused!
Has there just been a change in the relevant regs, or is the argument that we have been applying them incorrectly all along?
That is the way I see it.Yet another debate caused by ambiguous wording in the book.
I think I may have changed my mind on this, and take it that the supplies to other buildings bit only applies to TN-S, not PME.
Err.....I think!
Whos we ? lol
But both 544.1.1 and 54.8 have the caveat "except where PME conditions apply"For pme it's not the c.s.a. of the meter tails that is used for Table 54.8, but the c.s.a. of the PEN conductor in the supply cable to the service head
For a supply on a standard cutout of 100A or less, the supply conductor will be 35mm or smaller. As such, the sizes for the earth conductor to the MET and onwards to the CU will be 16mm for a PME supply, and 10mm from the MET to where the gas / water enter (assuming the water is metallic). For a supply greater than 100A you should be asking the DNO
I'm confused - in blue book you are referred to 54.8 specifically "where PME conditions apply"But both 544.1.1 and 54.8 have the caveat "except where PME conditions apply"
Page 48 of the on-site guide simplifies thingsBut both 544.1.1 and 54.8 have the caveat "except where PME conditions apply"
That is the crux of the matter.
I take it to mean if the conductors are part of the PME system (i.e. the combined part) then table 54.8 and 10mm^2 or 6mm^2 etc do not apply, and no figures are specified within the wiring regs.
In all other cases - where the conductors have been separated (after the service head) then the conditions in table 54.8 and 544.1.1 are applicable.
If it did just simply mean "except for PME" then that would be the wording.
Why write the clause as particular to PME conditions, if they didn't mean where it is part of the PME (TN-C ) aspect.
Taking "except where PME conditions apply" to mean you can't use that table or regulation when dealing with part of the PME system fits the words, and the fact that the bonding size isn't specified.
Taking "except where PME conditions apply" to mean that the bonding size in the regulation and table isn't applicable to an installation supplied by a PME system begs the questions 1) what cable size should be used as 54.8 is "except where PME conditions apply" so what size for PME; and 2) why the "odd" wording, why not just say 'except for installations supplied from PME"?
The heading for table 54.8 says 'minimum csa of the main protective bonding conductor in relation to the PEN conductor of the supply' so surely that is the csa of the DNO supply cable combined neutral earth, which as was mentioned previously in a domestic supply would be 35mm or less?I am confused also!
The heading for table 54.8 says 'minimum csa of the main protective bonding conductor in relation to the PEN conductor of the supply' so surely that is the csa of the DNO supply cable combined neutral earth, which as was mentioned previously in a domestic supply would be 35mm or less?
So in @cliffed s case above I would have thought 10mm or equivalent in steel, the combined swa of the cable and cpc would be sufficient to cover that? But then what is the supply connected to wasn't it an existing ring final, in which case the earthing conductor from there would only be 3mm and as such undersize?
My brain hurts!
Ps @mainline I think pages 55 and 56 osg do a better job.
I don't think this is new ?I think this is wandering slightly, from early on in the thread the interpretation of the new Regulation 544.1.1 is what is being brought into question.
It isn't a new Regulation it has been reworked so you need to compare both you will then understand the core debate here.I don't think this is new ?
Damn, I missed a chunk.It isn't a new Regulation it has been reworked so you need to compare both you will then understand the core debate here.