Hello All
The wife wants not one, but two, yes, two of those NEFF slide n hide ovens you see on Great British Bake-Off. Not cheap at well over £500 each.
Anyway...can I run two off the 6mm cable coming from the consumer unit currently with a 16A breaker.
I was thinking of changing breaker to a...
Been told today by an nic chappy they no longer apply it even when conditions allow . Asked him for the reg and the reply was ( i dont know the reg but its in the red book ) .
Dear all
Looked a job today in a kitchen
Existing 6mm t&e supply on a 30a Wylex 3036
Lady of the house wants to change existing oven and put in 2 single ovens in one housing
What's the best method of feeding these off the 6mm
Can't do a double socket as it's only rated at 13 / 20 amps
Was...
Afternoon all been a while since I've posted.
at today's job I noticed 10mm meter tails with 6mm bonding and although my first thoughts were tails should be min 16mm and bonding 10mm
so at the risk of sounding stupid I couldn't find the exact reason why this was wrong as the 10mm would take...
Hi,
I was tasked to install a bathroom extractor fan by a plasterer who gives me lots of little jobs.
I arrived at the job, fan ready to be installed so I check bonding and see its 6mm, condition is fine and it's connected to a 3036 board.
I inform customer the bonding needs upgrading...
Alright folks
doing an EICR in a flat that is supplied in 6mm cable, on a 100amp main fuse. C2
is it up to the landlord to contact the electricity supplier to upgrade this?
Hi all how can I work out the current carrying capacity of a 6mm t&e in surface metallic trunking. I can only find clipped direct and enclosed in insulated wall using table guides
Hi there.
Just a discussion with a colleague.
Is it acceptable to use a redundant 30A cooker circuit wired in 6mm, and downsize to 4mm via JB for a kitchen radial?
For example, if there is one ring supplying a house and you would like to reduce the risk of overloading with all the...
Hi,
Hope you are all having a good Easter Bank holiday.
Saw this the other day and just wanted people's opinions/thoughts please. (I was there installing led floodlights to the front and rear gardens only).
6mm T&E coming from the C/U into and along the attached garage wall approx 8m run...
This is only the second time I have had to crimp 6mm cable. I remember the first time a couple of years ago I had problems. Again this time the connection just pulled apart in my hands.
After looking through the forum I can see that others have had the same problem specifically with yellow...
Evening all.
A customer has asked for a dedicated radial circuit to feed 4 2g sockets.
He has asked for the cable to be rated at 45amps as he said at times the hifi equipment may reach this current. He is very specific that he wants the cable rated at this as a minimum.
He has asked for the...
As above why is this as I have had a thought and a 20a 2.5 mm cable would be sufficient?
Even in my new built it has an oven and hob both 32a radials for each on 6mm cable? Each with a 13a plug on the appliance as diversity shows around 10a max.
so even with an upgraded appliance I don't see...
TNC-S system
60A BS1361 Fuse
16mm Tails
6mm Main Earth
6mm Bonding
Ze 0.30
PFC 0.9kA
So if the CSA meets the requirements of 543.1.3
s= sq route of I2t/k
Sq route ((900x900)x0.1)/115
I got the 0.1 from table 3A1 pg 319, looking at the graph it looks like its about 750A to blow in 0.1 but to...
Hi all,
Company I work for have moved into a new factory and asked me to wire up the work benches, properly this time as before they just used a selection of extension leads dragged across the floor.
Anyway. On the wall there is a 4 core 6mm SWA cable terminated into a rotary isolator fed...
Can somebody kindly explain the difference the above. I currently have 6mm T&E multi strand running from my main consumer unit of a 32amp mcb which then ties up to a junction box where I run SWA to my shed. I
i am busy replacing my old oven and hob, at present there is a ccu supplied by 6mm t/e. my new cooker and hob have both come suppliesd with 1.5mm t/e flex. is it ok to connect both cables from oven and hob to the ccu? the circuit is protected by 32a mcb an rcd, thanks
SO1
Hello all, just a quick one.
Could someone please recommend a suitable way of terminating 4 6mm 3 core cable in a weatherproof junction box. I was thinking 60 amp connector block but don't really like the idea of trying to jam in 4 conductors and have them all held on the same screw. My other...