6mm | Page 5

6mm

  1. G

    For Sale 20m 6mm 3 core swa

    for sale one 20m roll of 3 core 6mm swa cable £45 plus postage
  2. J

    6mm earthing conductor

    Seen something today while performing a fire alarm test at a relatively sized office that struck me as strange. Thought there was no better place to query it than here. Like I said decent sized office, 3 phase tn-c-s supply can't really say too much more about the installation because this...
  3. infinity

    6mm Brown/ Grey DC cable

    Where is the best place to buy brown/ Grey DC cable? 6mm need about 400M of each
  4. S

    63A 3-phase electrics possible through 6mm cable ?

    Hi, Is it possible to get 63A 3-phase through 6mm cabling/wiring ?
  5. S

    6mm Supply

    Saw a consumer unit on a top floor flat today which currently has what looks like a 6mm t+e cable as the supply on a 60a fuse. Meaning the earth is probably only 2.5mm. Now this has always been here and probably been done by the supplier i guess? Your thoughts please.
  6. S

    8.5 kw shower on old red/blue 6mm

    Coming across a few of these. Very small run of cable as cu is in kitchen just below bathroom but should be 10mm cable. Did the old cable used to be slightly bigger than the new stuff?
  7. M

    Hob and 2 single ovens on 6mm cable.

    Hi Guys. Got a kitchen jobs coming up and there is only a 6mm out to hob oven at the mo. New oven specified is 7.4kw and there is 2 single ovens at 3.4Kw each. Total Plate load is 14.2Kw. When I looked at job I thought I would run in another supply. But working it out with diversity all 3 will...
  8. M

    can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW shower

    Hi I have two 6mm csa cables in the loft each going back to a separate 30A mcb in the CU. One is redundant, the other goes to a broken 8.5kW shower. I want to fit a new 9.5kW shower and would like to join both 6mm cables together at a 50A dpst shower switch, then run a short length of 10mm csa...
  9. B

    16mm or 6mm

    Hi all Im currently on with a condition report and it's a tn-s earthing arrangement with a 6mm coming off the sheath into an earthing block then a 16mm from there to the cu, now would you put 6mm as main earthing conductor as this is worse case or 16mm as it goes into the board. Or shall I put...
  10. kingeri

    6mm Aluminium Tails, DNO says no supply listed at the address

    Evening all. Today I was invited to look at a friend's latest project, a town center workshop-----garage. He is planning on turning it into a furniture shop. He has had a 'handyman' in doing some work for him, including electrics. Apparently there was no fusebox at all and no lighting...
  11. S

    Roomstat Controls next to 6mm csa

    Hi, would running a digital roomstat cable next to a 6mm --- pump cable cause interference? Neither cable is shielded. Thanks, Rick
  12. D

    6mm Supply Authority Super Cable

    Went to look at a house to buy few months back and no gas so needed all electric. Re wire needed so looked into new electric heaters, ovens, showers, boilers etc. Noticed supply cables to consumer unit about and cut out seem about 6mm and cut out was 60 Amp. Was wanting to change to 100 amps...
  13. P

    6mm main earthing conductor and main bonding conductors

    Been asked to install an extractor in bathroom. Installing 30mA rcd spur outside covering all lighting and ext fan. Obviously notify building control and installation cert. what's people's opinions of listing as a departure from bs7671 on installation cert. obviously recommend upgrade to 16mm...
  14. E

    6mm supply to park home

    I have been asked to do a consumer unit change on a park home, 2x30amp 1x15amp 1x5amp, the supply form the meter is only 6mm, I am aware there are different regs in regards to theses installation. 6mm seems undersized, Is this acceptable?
  15. sparks55

    6mm meter tails

    Found this when going to carry out E.I.C.R today meter man had even put label on to show it was Neutral surely he should have failed it :mad:
  16. S

    Crimping 6mm T+E

    Hi Guys. So as the title says I recently had to crimp some 6mm T+E using yellow pre-insulated butt crimps. I have a pair of Engex ratchet crimping pliers, which work very well with red and blue crimps, but when I tried to crimp the 6mm the crimps could be easily pulled from the cable. I...
  17. Clark3169

    6mm down to 2.5? design question?

    Hi guys just want to run this one past a few of you genius dudes out there. Is the following ok...? 32amp mcb > 6mm cable > socket in loft > x2 2.5 (1 leg to underfloor heating in bathroom 13amp & 1 to summer element 13 amp both fixed) the socket has a shower pump permanently plugged into it...
  18. Ian B

    Using a 6mm T&E to feed a Ring Main

    I'd appreciate peoples views on this, including compliance or otherwise with the regs. I've come across a 1-bed flat where one ring main serves the small kitchen, and boiler & security alarm. The unusual thing is that the ends of the ring are then connected to a single 6mm T&E that runs back to...
  19. ETradesmen

    6mm pyro...

    Hello everybody, my name is Michael. Last week a landlord called me regarding a faulty electric shower that the company tried to re fit under warranty but told him that the cable supplying it was under rated so they couldn't finish the job... I went to take a look and the property being a...
  20. P

    SWA HELP- Problem terminating CW20 gland with 6mm SWA

    Morning Its been a while since I last terminated SWA and have come up against a problem. I have prepared the cable, and got to the point of installing the gland, my problem is I cant get the cone body part and clamping collars to screw together, thread wont bite. The parts are fine when the...

OFFICIAL SPONSORS