Could someone just check my maths and thinking please.
Induction Hob 7.2kw = 7200/230 = 31.3 A
Double Oven 6.6kw = 6600/230 = 28.7A
Total Load = 60A
Apply diversity
10A + 30% of remaining load
60 - 10 = 50 x 30% = 15A
Diversivified load = 10 + 15 = 25A
So a 6mm T&E on a 32A MCB will be ok...
http://www.canford.co.uk/ProductResources/ig/5653.pdf
SIGNET (AC) - PDA200E INDUCTION LOOP AMPLIFIER | Premier Farnell CPC UK
hi all
doing my first induction loop system
basically fire alarm guy advised me on what to do and sent me the above products
he told me to run a cable around the...
There's this motor that has recently developed a problem. The motor draws alot of current when running, close to three times it's rated load. Any clue to fixing it?
Hi,
I was looking at the MK switches as we wanted
them to match with the sockets.
But they only have a 32A switch which
matches, the 50A switch is quite large.
Will the 32A switch be ok for this induction hob?
Hi guys, firstpost here and would be really grateful for some clarification:
I am helping a friend install his new kitchen which includes installing a newoven and induction hob (links below).The existing oven was on a dedicated radial circuit with 6mm twin andearth cable, 32 amp breaker and...
Gents,
I hope somebody can help. I'm running some cable for my electrician to test and connect up. He is on Holiday for the next 2 weeks which is why I cant ask him. In order to save me running two cables from the fuse box can the one cable feed the induction the hob and cooker via fused spurs...
Help with electrical connections please , colours as follows brown,black, blue, white.the hob is pre wired.costumer has no installation manual because of house move and they bought the hob with them.
Hello,
I am in the process of having a new kitchen installed and included in that is replacing our gas hob with induction hob.
Currently I have a 32a MCB running less than 10M from the consumer unit via 6mm cable to the cooker switch where it connects to the oven.
I am wanting to know if I can...
Hi all,
I've trawled through the numerous postings/threads on here and elsewhere and am content with loading and diversity:smilewinkgrin:
We've been looking at the various induction hob and oven options available and I was surprised to see that you can now buy 13A "plug-in" induction hobs in...
Hi all, was wondering if anyone could help me with this. I have had a three phase induction motor rated at 85.8amps full load and voltage is 480volts connected in delta. My question is that when I was first starting up the motor it kept on tripping the main switch due to the inrush currents. The...
A friend has just text me and asked if he can put an induction hob (beko hic64402 t) on a plug. I've just downloaded the user manual and it states to use cable type h05rrf 3g 2.5.
I've just googled that and it came up as Chinese manufacturers/sellers.
Never fitted or worked with hobs before so...
Hi everyone, I've been asked by a work colleague of a friend to finish wiring her kitchen as her electrician has done a Houdini!
She is having a indesit double oven rated at 4.8kw and indesit induction hob at 7kw , the previous electrician has wired a 6mm t+e into the kitchen can I use this...
Just had a call from two of our men who are testing an agricultural dealership , they have found 100 + volts on one of the lighting cpc's .
To cut a long story short , they have cut around 2 and a half meters out of the 10 meter the circuit ( 1.5 T+E ) and have it laid on the floor . They say...
Hi Guys
Looking for a bit of info here. Been called to look at a job for a local kitchen company as there spark has done a dissapearing act.
heres what we have hes broke into the ring and added a 20A D.P switch fused spur for the slim dishwasher no issues
This is where the debate starts...
Hi all,
can anybody help me out?
ive been investigating an intermittent fault that causes the bottom rcd of a 20 way dual rcd cu to trip approx every 8/10 days. (Really annoying fault to trace)..
i used a mili amp clamp meter today to measure the leakage to earth from the bottom row and got a...
Ive been asked to install a new circuit for an induction hob. The customer doesnt have the appliance as of yet but after a little bit of searching i managed to find the technical info i was after. The total load is stated as 3.68kw, but it also states that there are 2 x burners rated at 1.4kw...
Have a customer made an enquiry about needing a 45A supply for a new AGA induction oven, as that is what is spec'd by the manufacturer. Explained diversity etc and said the existing 6mm supply will be sufficient, which he understands, but he is concerned that when the AGA installers turn up...
I am installing an AEG HK654200FB 7.4kW induction hob. It will be on its own 6mm radial circuit supplied by a 32a Type B MCB. After reading the manual for this particular hob it says that it has an extra power function which only lasts for a maximum of 10 minutes on each ring which if all were...
Fitted a new induction hob for customer last yr, and was there sat morning swapping some light switches for her when she mentioned that the one ring of the hob wont work with a certain pan but the pan works on the other 3 rings, and other pans work on the hob that wont work with the 1st pan...