i=p/u
hi ho, i just replaced replaced 8 gu10 50W bulbs in room as were blown. there is 18 on the one circuit plus 3 mini strip lights under benches very likely 18W each, they were all working when i left and when she left room she switched all 3 switches on 1 go and she said the fuse had blown, would you say by her switchen all on one go would of blown the 5A 1361 fuse ?? i personaly think to many but when you add it up its under 5 A
18 x 50W = 900W / 230V = 3.9A
3 x 18W = 54W / 230V = 0.23A so roughly 4A all in, which is under 5A
any input guys before you all go your local niteclub and dance like your up a ladder and fallling
HALERS lol BTW any scottish lads I hear the rep is "eyecandy" Might need to give her a wee call
Did a rewire on this kitchen a few weeks ago....lovely bird she was....we had to go back to put a new central heating timer on for her earlier today....slurp...lol..
well i think change the lamps is easies option, what about that fuse that allows inrush currents tel, do they exsist that will fit in 1361 fuse carrier. if i changed to 6A or 10A mcb wouldn't that mean the zs would change and maybe not meet the requirements.
i=p/u The steady current drawn by a lamp is when it is at its operating temperature which for incandescent lamps is around 2000 deg C the initial current draw at 25deg C can as as much as 5 -10 times the steady current. So switching all switches together gives a massive surge just like a motor starting current.
Put in the largest fuse permissible for the circuit cable and advise customer to switch the switches one at a time
If you uprate the fuse you need to confirm the Zs still meets the 0.4 disconnection time
so you with me platty in chancging the 5A fuse carrier to 15A as it is on 1.5mm t&e, its a dr's surgery so they can take instructions and only the sockets are rcd protected
Can you replace the cable with a 2.5 at the board then into an enclosure with a C type breaker in and then using the installed cable....out to the lamps?........
was thinking c type breaker too but why 2.5mm for 15A fuse. am i missing something reallly badly here.. do you think would still trip the blow 15A fuse, the type c breaker does sound the pigs ears
1.5mm T&E ref method C (clipped direct )or buried in masonry has a max current 20A page 228 BS7671 Max Zs 1.70 at 70 deg so 1.7 x 0.8 = 1.36
If Zs is measured at less than 1.36 at furthest point on circuit and cable is installed Ref method C then 15 Fuse should be OK
559.6.1.6 max overcurrent device for normal lighting circuits 16A
yep. got it platty (p) 282...thank you. :crazy:
Think a GU10 Lamp holder might not come under that regulation
i=p/u
Northern Ireland
bs 1361 fuse
Australia
i=p/u,
i=p/u,
TrueNAS JBOD Storage Server