A

amberleaf

O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 ÷ 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
Designing )- part ( 2 )
:6:
Ourcircuit is installed in a conduit which contains two-other-circuits
Ifwe look at Table ( 4C1 ) we see that a ratingfactor ( Cg ) of ( 0.7) must be used because the conduit now contains Three-circuits . Using ( column 2 ) from ( 4D1A) we can see that a ( 2.5mm[SUP]2 [/SUP])cable has a Current-Carrying Capacity ( It ) of ( 24A )

( Iz ) will nowbe ( 24 x 0.7 = 16.8A )

Dueto being Enclosed with other circuits a (2.5mm[SUP]2 [/SUP]) cable can only carry( 18.9A ) This is assuming that all of yourcables are fully loaded & operating at ( 70°C)

Veryoften your cables are NOT fully loaded .provided that they are operating at NO more than( 30% ) of their grouping rating factor they can be discounted .
 
Designing )- part ( 1 )
:6:
Letsus say a ( 2.5mm[SUP]2 [/SUP])cable is to be installed in an Area which has an Ambient Temperature of ( 40°C ) We can see Table ( 4B1) that a ( 70°C Thermoplastic Cable ) has tohave a rating factor of ( 0.87Ca ) Applied toit . This will give us the maximum current that the cable could carry withoutthe conductor temperature rising above ( 70°C . 24 x 0.87 = 20.88A ) Thisvalue is known as ( Iz )

( Iz ) is the current which a cable can carry Under itsInstallation Conditions .

Thisshows us that due to the cable starting at a Higher Temperatureit will require less current to take its Temperatureto ( 70°C )
 
Abbreviationsused in ( PV ) system .
:hurray:
STC )- Standard Test Conditions .
Voc)- Open Circuit Voltage .
Vmp)- Maximum power point voltage . ( this is voltage under load )
Isc)- Short Circuit Current .
Imp)- Maximum power point current ( this is current under load )

A Switch Disconnector must be provided to Isolate the ( PV ) array from the rest of the system . To avoid ElectricShock .
( PV ) array should be connected to the Switch Disconnector at the earliest Opportunity. The Switch Disconnector must be ( DOUBLE POLE ) & it is very important to ensurethat the Disconnector used to isolate the D.C.side of the system is rated for D.C. currents .

Whenswitching D.C. the circuit ( Creates a much bigger ARC & the switch has to be ABLE toCOPE with this )
Itis PERMISSIBLE to use a DOUBLE POLE circuit breaker to BS-EN 60898as a Disconnector .

Wherethe Installation consists of more than One String . Isolation must be providedfor each String . ( Which must be Readily Accessible)

Itis Usually a good Idea to provide Isolation as Close to the Array as Possible& also at the Inverter End .

D.C.)- The first Important thing to Rememberwith regard to ( PV ) panels is that they are ( ALLWAYSLIVE ).

Apprentices(- Solar Photovoltaic ( PV ) power supply system(s) Regulations - p/200

Yourusing . A.C. to D.C.
 
Section711. p/197 .

Exhibitions’ . Shows & Stands . :hurray:

Thissection is for use with any “ Temporary Installations “ used for “ Exhibitions .Shows . Displays or Stands “

Thesecan be Indoors or Outdoors . it must be remembered that the Section ( Only Appliesto the Actual Temporary Installations ITSELF )
NOTthe Installation of the building from which the ( SUPPLY MAY be TAKEN ) ◄► Also it does NOT Apply to MOBILE UNITS

Theproblems surrounding this Type of Installation are it is Temporary . & becauseof this it is NOT Usually FIXED to be PERMANENT STRUCTURE .
Thiscould result in Mechanical Stress ◄► due to Movement of the STRUCTURE ( Plus general Public )

Dueto the Nature of this type of Installation . The wiring system must be well protectedfrom Mechanical Damage .

Wherethere is Access to the General Public . flexible cords must be very wellprotected against Mechanical Damage . Where the building which is being usedfor the Show or Exhibition Stand does NOT have a FIRE Alarm system . flame-retardantcables . conduit or trunking must be Used . & cables should NOT be joinedunless it is in ( An Accessory ) Thetrunking & conduit must have protection to a minimum of IP4X .

Switchgear& Control gear must be placed in an Enclosure . which can only be ( Openedby the Use of a Key or Tool ) This is unless they are Intended to be used by anOrdinary Person . This means of Isolation for the Show or Exhibition Stand mustbe readily Accessible to the User of the Stand .

Thissection of the Regulations also states that ( Where an Electric Motor may giverise to a Hazard it must be provided with an Effective Means of Isolation )

TN-C-Ssystems must NOT be USED & must be converted to a ( TT System : TN-S Systemmay also be Used )

TheSupply to the Temporary Structure must be Protected by a ( Time-delay or S-type RCD which has a Maximumrating of 300mA ) This is to provide Discrimination for Final Circuit(s) All other Circuit(s) apart from ( EmergencyLighting Circuit(s) must be Protected bya 30mA RCD. )

AllMetal parts which can be ( Accessed from within the Stand ) must be Bonded tothe ( MET ) within the Unit .

Aswith all other Electrical Installations .consideration must be given to Heat . This could be generated by the ElectricalEquipment & could cause Danger . Damage or Fire . to materials whichsurround it . or it could be an External Source of Heat which could causesimilar Damage to the Actual Electrical Installation .

SocketOutlets must be Installed to Reduce the ( Use of Trailing Leads ) Where socketoutlets are Installed in the Floor they must be protected from the ( Ingress ofWater ) & Mechanical Damage from Person or Equipment passing across them .

 
2392-10(- Spurs

MK . ( The Spur has a Hole in the Fuse carrier forpadlock ) :bulb2:

WhenServicing or Repairing Appliances ( Fuse Carries ) Spur’s. Connection Units can be Padlocked for AdditionalSafety .
(Fuse – Carriers can be Locked Open using a Padlock . list No – K2000 )

Spur(s) “ I now there saying put the Fuse in youPocket . Etc . by using a MK . Padlocked Off / You have Safe Isolation .

Justto make you Aware off it .


 
2392-10:

UsefulJunk .

Regulation415.1.1. ( The Whys !! )
:19: Domestic Installation . We all use cables with ( ThermoplasticPVC ) Insulation that are NOT Mechanicallyprotectedor ( Incorporate an Earthed metallic covering ) These cables would require RCDprotection .

Regulation415.1.2.
Theuse of RCDs is notrecognised as a ( SOLE MEANS ) ofprotection & does not obviate the need to Apply one of the protectivemeasures specified in Sections 411 to 414

411: Protective Measure . ( ADS ) Automatic Disconnection of Supply.
ProtectiveMeasure )- Where this protective measureis applied . Class II . equipment may also beUsed. ( 2392-10 / Bathrooms )

AsDesigners . 2392-10 .
Five Installation methods areoffered for “ Cables “ at a Depth of Less than (50mm )
Regulation. 522.6.6.

i) The cable should incorporate an Earthedmetallic covering . ( Which acts as a Circuit Protective Conductor) CPC
ii)The cable should be Enclosed in Earthed Conduit.
iii)The cable should be Enclosed in Earthed Trunkingor Ducting .
iv)The cable should be ( Mechanically protected ) againstpenetration by . Nails or Screws . ( -&-s . 2392-10 – Exams . plus / part – P )
v) The cable should be Installed in a SafeZone .

Weall Thing we know it all . But we don’t . ( The more you put IN – The moreyou get OUT)
That’swhy . we have Guidance note 3 . O.S.G. / Part – P . 17[SUP]th[/SUP] Edition – BritishStandards . Etc. “ We are still all Learning “
 
DomesticInstallation(s) – 2392-10 .
Studpartition walls / Brick / Block & PLASTER WALLS . :19:

Concealedcables requiring RCD protection ( ADS ) Rememberthat an Earth is the Most Important Arsenal youhave with an RCD . “ Under / Fault Protection “
 
2392-10: :19:

Itis a Legal Requirement that the ( Statutory Document) Electricity at Work Regulations 1989 . is Adhered to & that ( Installation(s) are SAFEto USE .

&Do Not Cause any “ Danger

The( Non-Statutory )documents .

17[SUP]TH[/SUP]Edition – BS-7671:2008 ( British Standards ) in a Court of Law .

Onsite–Guide … ( Guidanceonly )
O.S.G.– p/7 )- The scope generally follows that of BS-7671 . it includes material NOT included in BS-7671 .
Provides“ Background to the Intentions of BS-7671 “ &gives other sources of information .

Wording(- This guide does Not Ensure Compliance with BS-7671:2008 . it is a SimpleGuide ( in Plain Words – it isreturning us back to the 17[SUP]TH[/SUP] Edition – BS-7671:2008 ( British Standards ) in a Court of Law .

GuidanceNote – 3 )- Inspection & Testing : Are Not Legalrequirements . But by following them we are deemed to be Complying withthe Electricity at Work Regulations 1989 .
 
2392-10: p/17 :beatnik:

Approved Document P . is called“ Electrical Safety
&will be complied with if the Standard of Electrical Work meets the “Fundamental Requirements of Chapter 13 of ( BS-7671:2008)

Compliancewith PART – P
Inthe Secretary of Statesview . The requirements of Part – P will be METby adherence to the “Fundamental Principle’s “ forachieving safety given in ( BS-7671:2008 )

Toachieve these requirements Electrical Installations in Dwellings Etc . ( MUSTBE )

Designed & installed toafford appropriate protection against Mechanical & thermal damage . &so that they do not present Electric Shock & Fire hazards to people .
Suitably ( Inspected & Tested) ◄► to verify that they meet the relevant equipment & Installation Standards.
 
2392-10: ( In the Eyes of BS-7671:2008 – Competent Person)
:81:

IntegralTest Device : GN-3 . p/57 .

AnIntegral Test Device is incorporated in each RCD . This device enables thefunctioning of the ( Mechanical Part ) of the RCD . to be verified by pressing thebutton marked ( T ) or Test .

GN-3)- are telling YOU as a TESTER . ( Please Note)
OPERATION – of the IntegralTest Device [ DoesNOT provide a Means of Checking ] ◄◄◄◄◄◄◄

► TheContinuity of the Earthing Conductor or theAssociated Circuit Protective Conductor(s) .or
► AnyEarth Electrode or other means of Earthing . or
►Anyother path of the Associated Installation Earthing. or
►TheSensitivity of the Device.

The RCD Test Button )- Will only OPERATEthe RCD if is ENERGISED.
 
Code ofPractice : ( CoP)
InService Inspection & Testing .

AllInspected / Tested electrical equipment must carry a Label detailing .
-Date of Inspection / Test .
-Name of Inspector .
-Date of Next Inspection / Test .

Ever thing has a Reason . ??
AllNew Equipment NOTyet requiring Inspection / Testing must carry a Label detailing .

-Date of First Proposed Inspection / Test . ( It will work it’sway into the System )
:rockon:
 
Inspection& Testing .. ( PIR) :43:

2392-10. You may be sitting you 2392-01 Exam . Inspection & Testing -&-s This does come under PeriodicInspection Report.

Forthe Sake of -&-s )- The purpose of PeriodicInspection & Testing is to determine whether the (Installation is Safe for CONTINUED USE )
 
Inspection& Testing . 2391-10

Arethere any Legal Requirements for Electrical Inspection . ( PIR )

BS-7671:2008– Red Cover .
Requirements for Electrical Installations 17[SUP]th[/SUP]Edition . Require that “ Every new installation & Alteration or Extensionto an Existing Installation be Inspected &Tested before being put into SERVICE .

Electricityat Work Regulations 1989 – State .

i)As may be necessary to prevent danger . All system shall be maintained so as toprevent . so far as is reasonably practicable . such danger . Regulation 4 (2))
ii)System “ Means “ An electrical system in which allthe electrical equipment is . or may be . Electrically connected to a ( Common Source ) of electrical energy & includessuch source & such equipment . Regulation . 2 (1))c
iii)Electrical equipment – includes ( Anything Used) intended to be used or ( Installed for Use )to generate . provide . transmit . transform . rectify . convert . conduct .distribute . control . store . measure or use Electrical Energy . Regulation 2. ( 1 ))

Regulation621.1 . Periodic Inspection & Testing . ( PIR )

Whererequired . periodic inspection & testing of ( EveryElectrical Installation ) shall be carried out in accordance withRegulation . 621.2. to 621.5. in order to ( Determine ) So far as isreasonably practicable . Whether the installation is in a ( Satisfactory Condition for ContinuedService )

Igot this on 2392-10 )- 621.2. ( PIR ) -&-s
PeriodicInspection . comprising of a detailed Examination of the Installation ( Shall be carried out Without Dismantling or with PartialDismantling as Required )

2392-10. ( PIR )
Certification& Report . 634.1. p/163
Periodic Inspection Report .together with a Schedule of Inspections & a Schedule of Test Results .

1[SUP]st[/SUP]Amendment to the 17[SUP]th[/SUP] Edition . Red Cover. is still in use till then
:43:
Itbecomes effective from January 2012 .
Themost significant change is to the Certificates& Reports used for Inspection & Testing .
 
Fundamental Principles.
Regulation . 131.2.1. Two-basic methods by which basic protection can be Accomplished .

• Preventing a current from passing through the body ofany person or livestock .
• Limiting the current which can pass through a body toa Non-hazardous value .
 

Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
276
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
780

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top