A

amberleaf

O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 ÷ 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
Ihave NOT got . ( First Amendedment ) Green / am working off . Red Edition

2392-10. -&-s are looking for .??? Example . BS-7671: 2008 .333 / 337

ElectricalInstallation Certificate : ( EIC )

ThisReport is only Valid if a Schedule of Inspection(s) & a Scheduleof Test Result(s) . 2 x :leaving:


PeriodicInspection Report : ( PIR ) - To be appended to the Report .

(PIR ) Firstly )- Reporting on the Condition of an Existing Electrical Installation . -&-s :13:

ThisReport is only Valid if a Schedule of Inspection(s) & a Scheduleof Test Result(s) . are appended .

PS.Am not working to NICEIC. Test Sheets


 
WanderLead ( R2 )

Megger- 1552 . Megger / Wander Lead 50m ( 1.17Ω ) Not Nulledyet . :leaving:

Megger- 1552 . “ Auto – Null “ . 0.00Ω

Apprentices. it is Important to Null out any Lead before you startany work .

TestMethod 1 . Will yield : ( R1 + R2 ) GN-3. p/34
TestMethod 2 . Will yield : ( R2 ) GN-3 .p/35

TestMethod ( 1 & 2) are alternative ways of Testing the Continuity of ProtectiveConductor

Scheduleof Test Results ( R2 )
Scheduleof Test Results ( R1 + R2 )

Two methods may be adopted forthis Test but t is Important to Note : that when Testing the Continuity of ( CPCs ) with respect to ( SupplementaryProtective Bondingconductors . WhereRequired ◄◄ ) & MainProtective Bonding Conductors that in order to avoidParallel Paths .

Parallel Paths / it isnecessary to disconnect one end of the conductor in each Case to Obtain anAccurate value .

Parallel Paths ( Parallel - Circuit(s) has more than One Resistor ( Used as a Figure ofSpeech ) . ( Anything that UsesElectricity to do Work ) Learning Curve.
getsits name from having MultipleParallel Paths . to move along .

TheWhy’s / MultipleParallel Paths - This is done so that Lights don’t stopWorking . Yeah

• Fromthis Equation is that the more Circuits you add to a ( ParallelCircuit ) – The more thing you Use : Division of Installation / 314 . Dividedinto Circuits . Etc
TheLower the Total Résistance becomes . Rememberthat as the Total Résistance decreases . The Total Current increases . So ; themore things you Use . the more Current has to flow through the Cables in the PlasteredWalls .

TheInverse of the Total Résistance of the Circuit . ( Effective Résistance ) isequal to the sum of the Inverses of the Individual Résistance .

1/Rt = 1/R[SUP]1[/SUP] + 1/R[SUP]2 [/SUP]+ R[SUP]3[/SUP]+ …. ( This one come around on 2392-10 Exam )

UsefulJunk .
OhmsLaw . may be used in a ( Parallel Circuit ) aslong as you remember that you can use the formula with EitherPartial values or with Total Values . don’t mixparts

V – Total = I total : R total .
V –Part = I part : R part .

- Thepotential drops of each circuit equals the potential rise of the source .

V[SUP]T[/SUP]= V[SUP]1[/SUP]= V[SUP]2 [/SUP]= V[SUP]3[/SUP]= …..

- The total current is Equal to the sum of thecurrent in the circuits .

I[SUP]T[/SUP]= I[SUP]1[/SUP]+ I[SUP]2[/SUP]+ I[SUP]3[/SUP]+ …..
 
Informationfor Inspector . 2391-10 .

RequirementInformation . Regulation . 610.2 . :38:

BS-7671:2008. requires that the followinginformation shall be made available to the person or persons carrying out theInspection & Testing .



 

2392-10: Handy in yourExams . :19:

RingFinal Circuit(s)

Statethe effect on Conductor Résistance when cablesare Connected .

Whencables are connected in Parallel the overall Résistancewill be Less than the Résistance of the conductor of the lowest value .

Theformula for Calculating Résistance of Conductor(s) in Parallelis ??

1/R[SUP]T [/SUP] =1/R[SUP]1[/SUP] + 1/R[SUP]2 [/SUP] + 1/R[SUP]3[/SUP][SUP] [/SUP]+ …..

Where( RT ) is the overall Résistance .

R[SUP]1 [/SUP], R[SUP]2[/SUP][SUP] [/SUP], R[SUP]3[/SUP][SUP] [/SUP], Etc. are the Individual Résistancevalue of each conductor for as many conductors that are Connected in Parallel

Example:

Threeconductors of Résistance ( 1Ω , 2Ω ,& 4Ω ) are connected in Parallel . Calculating the total overall Résistance .

1/R[SUP]T [/SUP] = 1/R[SUP]1[/SUP] + 1/R[SUP]2 [/SUP] + 1/R[SUP]3 [/SUP][SUP] [/SUP]

1/R[SUP]T[/SUP][SUP] [/SUP] = 1/1 + 1/2 + 1/4 .

1/R[SUP]T [/SUP] = 1 + 0.5 + 0.25

1/R[SUP]T [/SUP] = 1.75Ω ( 1 ÷ 1.75Ω = 0.57Ω )

1/R[SUP]T[/SUP][SUP] [/SUP] = 0.57Ω








 

2392-10: Handy in yourExams . ( TT System ) ◄◄◄ :19:

Measuringusing Earth Electrode Test Instrument )

ThreeMeasurements are taken : 79Ω + 85Ω + 80Ω

Addedal Together ( 244Ω ) …………… 244Ω ÷ 3 = 81.33Ω

Why( 3 ) 3 / Rods . Yeah :chillpill:




 
2391-10: Ring Final Circuit . :26:

• Statethe relationship between Conductor length & Conductor Résistance .

Résistance. in Ohms , of a Conductor or Cable Increases with Length .


• InsulationRésistance . :yesnod:

Variationin Cable Length .

Asa Cable increases in length . unlike the conductor résistance which increaseswith length . Insulation Résistance decreases with length .

Theformula for calculating ( New Value ) of Insulation Résistance is as follows .

InsulationRésistance = Original length x InitialInsulation Résistance . / New Length

Example:

ACable of length ( 50m ) has an Insulation Résistancevalue of ( 200MΩ ) .
Ifits length is increased to ( 100m ) . Calculate its Insulation Résistance

InsulationRésistance = Original length x InitialInsulation Résistance . / New Length

=50 x 200 ---- 100

=10.000 ----- 100

= 100MΩ





 
Somethingto think about . Yeah . :yesnod:

Insulation Résistance

Statethe precautions to be . taken before testing Insulation Résistance in Terms of.

i)Isolation of circuit(s) & equipment .
ii)Voltage sensitive equipment .
iii) Electronic components .

a)Isolate of circuit(s) & Equipment .

1)Select a ( GS-38 ) ApprovedTest Lamp or Voltage Indicator .
2)Check ( Test /Lamp / Voltage ) indicatoris functioning correctly by testing on a ( Known Supplyor Proving Unit )
3)Determine whether Isolation is for ( Whole Installation or ( Specific Circuit(s) .
4)Locate means of Isolation ensuring there is no ( Standby Supply Arrangement )
5)Switch ( OFF & Lock OFF Isolation device(s)e.g. Fuses Switch . Isolator . MCB .
6)Verify . ( Using Test Lamp / Voltage Indicator. Circuit(s) are Dead between Line(s) Neutral & Earth.
7)Erect ( Warning Notice(s). in appropriate position(s) . 2392-10 . atConsumer Unit .
8)Re-check ( Test Lamps / VoltageIndicator ) is still functioning correctly .
9)Retain Key(s) . for Locking OFF Devices /

b) Before carrying out InsulationRésistance Testing it must beestablished that there is ( No Voltage Sensitive Equipment Connected ) thatmay be damaged or Malfunction because of the test voltage applied .

Examples:
Maybe Computers . Programmable Logic Controllers ( PLCs ) Programmers . etc. .

TheEquipment would either have to be disconnected during test . ( Testing / 612.3.3 ) ……….. PLUS – Note . Wherethe circuit includes Electronic Devices .

OrInsulation Test with Line(s) & Neutral connected together & Test between theses& the Protective Conductor .

c)Before carrying out Insulation Résistance Testing it must also be established that there is ( No Electronic Components ) that may be damaged ormalfunction because of the Test Voltage Applied .

Example - Dimmer Switch . This would have to beRemoved during test & the switch wires connected together .

- Describe Methods of Testing Insulation Résistance :

Beforecarrying out Insulation Résistance Testing ensure that . ??

1)All lamps . capacitors & loads are disconnected .
2)Voltage sensitive electronic equipment such ad Dimmer Switches . Touch Switches. Delay Timers . Power Controllers . Fluorescent lamps starter . Emergency Lighting . RCDs are disconnected .
3)There is No Electrical Connections between Line(s) . Neutral &Earth .



 
Useful Junk . ( If )

2392-10 :
RCD . the contacts will Automatically be Opened . Thereby providingagainst Electric Shock . The Term . “ RESIDUAL “ in Residual Current Device implies that ( There) is a residual current flowing in the ( Circuit )Over & above that required to provide ( Power to aLoad ) :yesnod:

 
2391-10 : ( This maybe helpful in Exams ) WORDING . Yeah :6:

612.2.1. Continuity ofProtective Conductors :

Protective Conductors .

Describethe need for . & Methods of . verifying the ( Continuity) of Protective Conductors & the “ Interpretation of results. ◄◄ :willy_nilly:

Answer

TheContinuity of the ProtectiveConductor is very important since it ( Forms Part) of the Earth Fault Loop Path .
Inthe event of a Fault to Earth the Faultcurrent flows through the Protective Conductors& the Earth Fault Loop Path as a whole .
Ifthe impedance of the Path was too high the Fault current may not be largeenough to operate the Protective Device thusresulting in ( Exposed Metalwork becoming Live )due to the circulating Fault current .




 
2392-10: :6:

Question.

InsulationRésistance . ( IR) Table 61 . :willy_nilly:

SELV & PELV (- upto ( 50V ) or ( 120V d.c. )

SELV ( Howdo I know / p/31 – Regulations . ) Extra – Low .


Describe the Test to Verify Separation between ( SELV ) circuits & other circuits ( -&-s )

SeparatedExtra Low Voltage ( SELV ) circuits operated at voltages up ( 50V ) or ( 120V d.c. ) This voltage can be obtainedin a number of ways such as a ( Double / Wound Transformer ) having a supply primary coil connected tothe 230V a.c. . Supply & an outputsecondary coil at the required Extra Low Voltage .
Thetwo coils are not & should not be connected in a ANY way 7 a test must be carried out to prove this .

Byusing an Insulation Resistance Tester . set to ( 250Vd.c. ) test voltage on the ( MΩ ) rangecarry out the following test procedure . With the transformer disconnected fromthe supply connected one test lead to the Primary coil & the Other testlead to the secondary coil .

Pressthe test button & note the reading in ( MΩ ) .

Tocomply with BS-7671:2008 . This reading should be no less than ( 0.5MΩ )
 
Apprentices:

Inspection & Testing . :coolgleamA:

Whatis the definition of Inspection .
Inspectionis a general term that can have a wide variety of meaning . Will usually bemore specific / VisualInspection or Non-destructive Testing .

GN-3p/63 . ( PIR )
621.2.
Theformal Inspections should be carried out in accordance with Chapter 62 ofBS-7671 . This requires an Inspection comprising careful scrutiny of the Installation. carried out without Dismantling or Partial Dismantling as required .together with theAppropriate Tests of Chapter 61 .

EarthFault Loop Impedance .
TheImpedance of the Earth Fault Loop . Line - to - Earth Loop . Starting& Ending at the point of Earth Fault .

RingFinal Circuit . Final Circuit arranged in the form of a Ring & connectedto a Single Point of Supply .

ResidualCurrent Device . ( RCD )

( Residual / Dual . meaning two . Line& NeutralTwo liveconductors .

ItUses the Idea that the Current in the Line &Neutral must be Exactly the Same . Yeah ( Balanced )

TheRCD does is compare the Current in the Line& Neural . If they’re not Identicalit Trips Out .


 
2392-10:

Regulationsinitially call for Visual Inspection . but someItems such as Correct Connection of Conductors .
Canbe done during the actual Testing . :coolgleamA:
 
2392-10.

O.S.G.p/86
612.7. EarthElectrode Résistance . ( Ra ) - 200Ω

612.7. : Electrode underTest is being used in conjunction with an ( RCD)

A Loop Impedance Tester ( Zs )

TTSystem(s) . The value of the Earth Electrode Résistance ( Ra ) in Ohms. Multiplied bythe Operating Current in Amperes of the Protective Device . ( I∆n ) should NOTexceed ( 50V ) ( Ra ) = 200Ω . Then the maximum RCD operating Current should NOTexceed ( 250mA ) :coolgleamA:

 
Apreferred sequence of Tests is recommended . Where Relevant . 2392-10 :willy_nilly:

TN-S / TN-C-S .

612.2.1. Continuity of protective conductors .
612.2.2. Continuity of Ring Final conductors .
612.3.Insulation Résistance . ( IR )
612.6. Polarity .

612.7. Earth Fault LoopImpedance .
612.10. Additional Protection .
612.11. Protective Fault Current . ( PFC )
612.13. Functional Testing .
 
Last edited by a moderator:
2392-10.

Lets make the Books work for Us . O.S.G. p/166 . Table 9A .

612.2.1. Continuity of ProtectiveConductors .

AllProtective Conductors . including Main Protective Bonding Conductors &Supplementary Protective Bonding Conductors . ( Where Required )

ConductorSize ( mm[SUP]2[/SUP] ) 2.5 : Résistance ( mΩ/m ) 7.41 .
ConductorSize ( mm[SUP]2[/SUP] ) 4.0 : Résistance ( mΩ/m ) 4.61 .
ConductorSize ( mm[SUP]2[/SUP] ) 6.0 : Résistance ( mΩ/m ) 3.08 .

ConductorSize ( mm[SUP]2[/SUP] ) 10.0 : Résistance ( mΩ/m ) 1.83 .
ConductorSize ( mm[SUP]2[/SUP] ) 16.0 : Résistance ( mΩ/m ) 1.15 .


I WorkingLong Hours . Sunday is the Only DayOff .

I do Apologize if I make any Small Mistakes . Thank youfor Understanding . :willy_nilly:
 
ASimple Résistance test between the Ends of the Line . Neutral or Circuit Protective conductors willonly Indicate that a Circuit Exits .

Whetherthere are Interconnections or Not .

Same value whatever diameter is measured .

(L1 / N2 ) ↔ ( N1 / L2) Circuit formed by Cross- connection .

InitialVerification :
Aftercross connection of Line & CPC you’d check between Line & CPC at every Socket & Spurs would becomeApparent . ( Spur ) will give a Higher Reading .Ω


Apprentices: ( Firstly – You Reading confirms thatthere is No Open Circuit on the Ring Final Circuit) Yeah .

RingFinal Circuit . ( Dead Test )

Instrument: Set on Ohm’s .

Under(- Schedule ofTest Results .
CircuitLoop Impedance Ω
RingFinal Circuit / Only measured – ( End to End )

Line/ Line - Little ( r1 ) = 0.43Ω . Measured – ( Endto End ) Bigger Copper / Lower Résistance .
Neutral/ Neutral - Little ( r/n ) = 0.42Ω . Measured – ( Endto End ) Bigger Copper / Lower Résistance .

CPC/ CPC - Little ( r2 ) = 0.73Ω . Measured – ( End to End ) SmallerCSA / High Résistance


Topquark. I can’t Editany Post . on my Section(s) Thankyou . :coolgleamA:



 
OhmicValues (- 70m Ring Final Circuit . –wired in 2.5mm[SUP]2[/SUP] / 1.5mm[SUP]2[/SUP] Twin . T&E ) :willy_nilly:

Readings at Each Socket . Examples Only.

Measurements. L1 / L2 . 0.26Ω - ( 0.015Ω )
Measurements. N1 / N2 . 0.26Ω - ( 0.015Ω )

Measurements. CPC -1 / CPC - 2 . 0.32Ω & 0.34Ω . - ( 0.02Ω )

ForSpurs . each metre in length will add the flowing résistance to the above values.

 
Polarityis towards the end of the recommended test sequence . 612.6 :svengo:

Polarityon the Ring Final Circuit conductors is Achievedsimply by conducting the Ring Circuit Test .

Asfor Radial socket outlets . (- Continuity of the CPC will have already been Proved by linking Line& CPC & Measuring between the same terminalsat each socket .
OnlyLine / CPC reversalsneed to be Checked .

612.2.Continuity of Conductors . We are conducting this Test at the same time as thatfor Continuity of CPCs . ( In Theory ) :bulb2:

Wedo this for Ring Final Circuit . CPCs End – End
Wedo this for Radial . Line / CPC

( In Theory ) Radial Circuit . Line / CPC . we are using Wander Lead Return .

Linkingtogether Line & Neutralat the Origin & Testing between the same Terminals at “ Each SocketLine / CPC reversalwill result in NO Reading at the Socket inQuestion .

Lighting Polarity (- Link at Consumer Unit ) Line & CPC – Pendent Set . ( Polarity / proved by Operating Switch ) Switch wire / CPC . Switchis Opened & to confirm then Closed Polarity



 
2392-10: :aureola:

Statethree different types of Protective Conductorthat are commonly connected to the Main Earth Terminal ( MET ) of an Electrical Installation .

i)Earthing Conductor .
ii)Circuit Protective Conductor .
iii)Main Protective Bonding Conductor .
 
Self-employed Electricians going to working in Industry . :crazy:

The Pop Up machines now come under the ( PAV ) Category ( Push Around Verticals )

Which also includes the ( 1a ) Category .This course can be done solely for these .

But be more advantageous for you to dothe ( 3a ) Category ( Scissor Lifts ) whichwould also cover you for using the ( PAVs ) and any in the ( 1a ) Category . proving that you have had “Familiarisation “ on them .

What your needing . ( PAL ) Powered Access Licence .
Type ( 3a / 3b ) ◄◄

IPAF : ( 1 person ) One Day Course .Training £ 228.00 – Vat paid

Lasts : 5 Years .

This will show you the Machines to Use . WWW.ipaf.org
 
FourDocument that the ( Inspector ) may need to consult during the Inspection& Testing procedures . :vanish:

BS-7671:2008.
IET– Guidance Note – 3
IET– On – Site – Guide .
TheElectricity Safety Quality & Continuity Regulations 2002 .
 
Inspection& Testing of Electrical Installations . :vanish:

Usingdiagrams to support your answer explain the three steps required to perform aContinuity of Ring Final Circuit Conductors Test.

Explainany precautions & checks you would make before starting the Test .

Using (- A Low résistance ohm-meter continuity tester will beused for this Test .

WithTest Leads & Probes conforming to HSE . GN-38
Beforeany measurements are taken the résistance value of the Test Leads .
&Probes are noted & this value is subtracted from any Test Results . Alternatively if the Test Instrument has anAuto null facility this should be applied before any measurements are recorded.
Withthe electrical installation safety Isolated& Proved Dead.

Indentify& disconnect the Line . Neutral . & CPCconductors of Ring Final Circuit at the Distribution Board .

Measure& Record the End to End résistance of the following.

Therésistance of the Phase to Line Loop = (r1 )
Therésistance of the Neutral to Neutral loop = ( r/n )
Therésistance of the CPC to CPC loop = ( r2 )

Thevalues of ( r1 + r/n ) & r2 willindicate whether the conductors are continuousor not .

A FiniteSmall reading will indicate the conductors are continuous .

A high Résistance value will indicatethe conductors are Open Circuit . or Faulty . orConductor terminations are loose .

TheLine & Neutral conductors both being typically 2.5mm[SUP]2 [/SUP] should have equal values of résistance:- Measured within 0.05Ω of each other .within 0.05Ω
Wouldalso apply if the Ring Final Conductors were larger ( 4.0mm[SUP]2 [/SUP] ) CPC being 1.5mm[SUP]2 [/SUP] . for
2.5mm[SUP]2 [/SUP] / 1.5mm[SUP]2 [/SUP] T&E - has a smaller Cross-sectional area than theLine 2.5mm[SUP]2 [/SUP] conductors . As suchthe CPC résistance will slightly higherthan the Line conductors’ .

2.5mm[SUP]2 [/SUP] / 1.5mm[SUP]2 [/SUP] T&E - The résistance of the CPC should beapproximately ( 1.67 times ) greater than the résistance of the Line conductors.
Performa quick calculation to check the Expected value of the CPC is approximately ( 1.67times ) larger than the Line Conductors .
 
Whattype of Inspection & Tests . Will be required for the ElectricalInstallation within this building . ?? :oops:

Forthe ( NEW ) Electrical Installation . an InitialInspection Test & Verification
Forthe ( Existing ) Electrical Installation . anPeriodic Inspection report & Test .

Listall the relevant documentation that need to be competed for this ElectricalInstallation . ??

( 2392-10 ) ► New ◄ Electrical Installation
i)Electrical InstallationCertificate .
ii)Schedule of Inspections .
iii)Schedule of Test results .

thistake you into 2391-10 ) ( Existing ) Electrical Installation
i)Periodic Inspection Report for an Electrical Installation
ii)Schedule of Inspections .
iii)Schedule of Test results .
 
Twopossible conditions that may have an Effect on the Measured value of ( EarthFault Loop Impedance ) :vanish:

i)Ambient Temperature in the locality of thecables Under Test .
ii)The Actual Temperature of the Cables Under Test .


 
Whatfunction does a Switch perform in the Circuit . :willy_nilly:

ASwitch ( Opens ) or ( Closes) an electrical circuit .

Ifthe Circuit is ( Open ) – NO electricityflows . “ Circuit is broken “

Ifthe Circuit is ( Closed ) - Electricity Flowsthrough the Circuit . 2392-10 ( Can we confirmPolarity ) “ Circuit is complete “

Sowhat is a Polarity Test .

Basicallyit is a Test that creates a Circuit using the Line conductor & the singlepole device in question . Breaking the circuit when Operating the device . means that the reading on theInstrument will Change .

&thus confirming that device must be connected in the Line Conductor .

Test to Ensure that all singlepole devices ( Fuses . Switches . & Circuit Breaker ) are connected inthe Line Conductor Only .


Switch: Permanent Live. Switch Live .

Switching T&E . You should sleeve the Blue Conductor / with brown sleeve .to say it is being used as a Switch Wire .

UsefulJunk .

Metal is Used in Switches because most Metals are Good Conductors of “ Electricity “



 
DomesticInstallation

Whatis - Circuit Control from a Testers point of View ? :willy_nilly:

Itis Vital that any Circuit . NO matter its levelof complexity . ( Can be Controlled )

Asimple Switch :- allowing us to turn the CircuitOn or Off .
 
Regulation/ Definitions – p/26 . Wording

Isolation :- “ Function “ .

Afunction intended to Cut Off for reasons of safety the supply from all . or a discretesection . of the Installation by separating the Installation or Section fromevery source of Electrical Energy .

Isolator :- “ Disconnector “

AMechanical Switching Device which . in the ( OpenPosition ) complies with the requirements specified for the Isolationfunction in part 2 of BS-7671 .

Note : it also States a“ a “ Isolator “ is otherwise known as an “ Disconnector “

 
Sourceof Supply .

Oftena circuit is Thought of as being the ( Load )& the conductors supplying the ( Load )
InReality they are only ( Part of the Circuit ) inorder for Current to flow two conditions have to be met .

i)There has to be a ( Potential Difference ) applied across the circuit ( Voltage )
ii)There has to be a ( Complete Circuit ) “Circle “ for current to flow around .

A Source of Supply can be ( A.C. or D.C. )

 
Apprentices.

Determiningthe Protective Device characteristics forCircuits . ??

ElectricalInstallation Design .
Allyou need to know is to use the given details to select the Appropriate Protective Device for a given circuit .

Themain formula we can start with .

Iz > = In > = Ib .

Ib (- design current of circuit ( A ) The loadto be connected to the circuit .
In (- Nominal current of the Protective Device ( A )
Iz (- Effective current carrying capacity ( A )

Thismeans that in every circuit at all times the current carrying capacity of thecables must be ( Higher ) than the highestpossible load current .
Also. the Protective Device rating must be ( Higher) than the load current but lower than the maximum current carrying capacity ofthe cable installed .



 
As-&-s are touchy about RCDs .

AResidual Current Device ( RCD ) will . ??
i)Operate if a Short Occurs between Line & Neutral
ii)Operate if a Small Overload occurs .
iii)Operate if Line& Neutral are out of Balance . ◄◄ “ Resi/ dual “ . Two Words - Line & Neutral
 
Regulation Red book 2008 : Chapter 53 :speechless:

Protection. Isolation . Switching . Control & Monitoring .

Regulation:- The “ Term “ Isolation & Switching – as used in BS-7671 ( Refers to four distinct functions )

i) Isolation
ii)Switching OFF for mechanical Maintenance .
iii)Emergency Switching &
iv) Functional Switching

Referto Table 53.2 – p/117

 
2392-10:- “ Consumer Controlgear “ 530.3.4. :speechless:

ForInstallation with a 230V single-phase supplyrated up to 100A that are under the control of ( Ordinary Persons) should either .

Comply with BS-EN 60439-3 & Regulation 432.1. of BS-7671.
Be a Consumer Unit – incorporating components complyingwith BS-EN 60439-3


 
Regulation Chapter 532 . :- Devices for Protectionagainst the Risk of Fire . :whatchutalkingabout

532.1.Where in accordance with the requirement of Regulation 422.3.9. it is necessaryto limit the Consequence of ( Fault Currents )in wiring system from the point of view of ( Fire Risk ) THE Circuitshall be either .

i)Protected by an RCD complying with Regulation 531.2. for ( Fault Protection ) &
- The RCD shall be installed at the ( Origin of the Circuit ) to be Protected . &
- TheRCD shall Switch all Live Conductors . &
-The rated Residual Operating Current of the RCDshall Not Exceed ( 300mA) ETC .









 
Chapter537 . Isolation & Switching .

Isolation– ( 537.2.
Switchingoff for Mechanical Maintenance - ( 537.3.
EmergencySwitching - ( 537.4 .
FunctionalSwitching - ( 537.5.

Fire-fighter’s Switches – ( 537.6 . :speechless:

A Fire-fighter’sswitch shall be provided in the Low Voltage circuit supplying :

i)( Exterior ◄ ) electrical installationsoperating at a Voltage Exceeding Low Voltage . &

ii)( Interior ◄ ) Discharge lighting installations operating ata Voltage ( ExceedingLow Voltage )

(Temporary Installation ) Fire-fighter’s Switches – ( 537.6.1.

Forthe purpose of this regulation . An installation in a CoveredMarket . Arcadeor Shopping Mall is considered to be an (Exterior Installation )
A Temporary Installation in a Permanent Building used for Exhibitions isconsidered ( NOT to be an Exterior Installation )



 
“ Isolation“ :icon14:

Itemsto be Considered in Relation to “ Isolation “ devices.

Number of poles to be “ Isolated“
“ Isolation “ of groups &inconvenience .
Devices designed and / orinstalled to prevent Unintentional or Inadvertent closure .
“ Isolation “ devices to beClearly Indentified and Indicate the Installation or Circuit it Isolates .









 
Isolationrequirements for ( TN-S ) Systems .

Single-phase. L N - Circuit Protective Conductor .

Three-phase. L1 . L2 . L3. ≈ N . - Circuit ProtectiveConductor .

 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
***Cont../ Useful Information for Electricians & Apprentices***
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
933
Unsolved
--

Advert

Thread statistics

Created
amberleaf,
Last reply from
Dan,
Replies
933
Views
96,654

Advert

Back
Top