O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer
FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory . Sowe are all in the Same Boat . “ To Learn “
For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag
CookerDesign Current Calculations
Thefirst thing you have to do is get Your Head around the Calculations !!
(From a Design point of View ) 2392-10
DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000
(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps
-Controlled via a CookerSwitch with a Socket outlet .
Asa Designer . we’ll have to Apply Diversity ??
Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .
TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors ) O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)
DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .
Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.
Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current ) The10A will be used at the End of the Calculations’
-So your Work out the Total Power Rating & then calculate the Full Load Current
Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW
I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A
132.6. Cross-sectional Area of Conductors . ( C.S.A. ) :rant: :rant: The Cross-sectional area ofconductors shall be determined for both normal operating conditions & .where appropriate . ( for Fault Conditions according to )
i) The admissible maximum temperature . ii) The admissible voltage drop . ( Vd ) iii) The electromechanical stresses likely to occur due to ( Short – circuit ) & ( Earth Fault Currents ) iv) Other mechanical stresses to which the ( Conductors ) are likely to be ( Exposed ) v) The maximum ( Impedance ) for correct operation of ( Short Circuit ) & (Earth Fault Protection ) vi) The method of installation . vii) Harmonics . viii) Thermal insulation .
thatare given in Chapter 13 are intended to provide for the safety of persons .livestock & the protection of property against dangers & damage whichmay arise in the reasonable use of electrical installations .
itis recognised that good workmanship by competent persons using proper materialswill reduce any hazards that may arise & that every item of equipment shallcomply with the Appropriate BritishStandard .
Electricaljoints are a potential source of overheating & if NOT securelymade could ultimately cause a fire . for this reason there are severalregulations relating to electrical connections .
Thisis mentioned within Chapter 13 . in regulation 134.1.4. Every electrical joint& connection shall be of proper construction as regards conductance .insulation . mechanical strength & protection .
“Good workmanship by competent persons using the proper materials will reducethe risk of Overheating or Fire . “
Regulation 526.3.requires that every connection shall be accessible for ( Inspection . Testing & Maintenance ) There are 6 exceptionsto the rule ( vi ) is .
Equipmentcomplying with ( BS-5733) for a ( Maintenance Free ) accessory & ( Marked ) with thesymbol ( MF) & installed in accordance with the Manufactures Instructions .
BS– 5733 . ( Defines ) a Maintenance Free accessory as :- Anaccessory which does NOT require further ( Inspection . Testing or Maintenance ) afterinstallation in a circuit . & which incorporates ( ScrewlessTerminals ) & cable clamps to secure any associated cables .
TheElectrical Safety Council Technical Manual States that a junction box with Screw Terminals must be ( ACCESSIBLE ) MUSTbe ACCESSIBLE . Thisis to allow ( Inspection ) of jointswhich could have relaxed or loosened over time . a potential problem withscrewed terminals . SO . unless provision is made for ( Access ) where boarding . carpet or other similar covering is laidover a ( JunctionBox ) it may not be consideredaccessible & maintenance free terminals should be Used .
Appendix15 of the Wiring Regulations which states “ Junction Boxes with Screw Terminals must be Accessible for ( Inspection . Testing & Maintenance ) or Alternatively . use Maintenance Free Terminals / Connection - Regulation 526.3.
“Junction Boxes with Screw Terminals must be Accessible for Inspection …… ETC
Regulation : 526.3. p/106
i) . ii) . iii) . iv) the Same
Regulation : 526.3. p/131 :christmastree1:
v) Joints or connectionsmade in equipment by the manufacturer of the product & not intended to be ( Inspectedor Maintained )
vi) Equipment complyingwith BS-5733 for amaintenance-free-accessory & marked with the symbol ( MF ) & installed in accordance with theManufactures Instructions .
Whenfitting recessed downlighters the following method would overcome all the issues .
Thesheath of both solid conductors & flexible conductors for the light fittingcan be secured as they enter the Enclosure . ThisEnables compliance with . Regulation522.8.5. in particular where it states that thereshall be no ( Undue Mechanical Strain on the Terminations )of the conductor(s)
Regulation 526.8. whichrequires the cores of Sheathed Cables from which the Sheath has been removed tobe Enclosed . can be seen to be complied with .
Cableclamps prevent Strain on Terminations for Compliance with Regulations .
Every cable or conductor shall be supported in such a way that itis not exposed to ( Undue MechanicalStrain ) & so that there is noappreciable mechanical strain on the terminations of the conductors . accountbeing taken of mechanical strain imposed by the supported weight of the cableor conductor itself .
Regulation 526.8. Connectionof multiwire . fine wire & very fine wire conductors .
Regulation 526.8.1. p/107. In order to avoid inappropriate separation or spreading ofindividual wires of multiwire . fine wire or very fine wire conductors .suitable terminals shall be used or the conductor ends shall be suitablytreated
Regulation 526.9.1. p/131 . Connection of multiwire . fine wire & veryfine wire conductors . In order to avoid inappropriate separation or spreading ofindividual wires of multiwire . fine wire or very fine wire conductors .suitable terminals shall be used or the conductor ends shall be suitablytreated
Requirements of 17th Edition Wiring Regulations – BS-7671:2008 .
A further potential problem can be found within the ( Junction Box ) concerning the type of conductors that are typicallyterminated . it is often the case in Domestic Installation(s) that solid twin & CPC cables will be used for the fixed wiring withthe conductor to the light fitting . Etc . or transformer if the lighting is ( ELV ) Being a ( Flexible conductor )
Strands of flexible cable are Secured adequately in the terminal& not been damaged to ensure compliance with regulation 526.2.
Asa Tester . How many time have you seen this . ?? . Q - Junctionbox :bulb2: Whenthe conductor was removed for (Inspection ) it is clear that some ofthe Strands have been damaged during termination .
MaintenanceFree Terminals , Theaccess to electrical connections should be adequate for their ( Safe ) &proper ( Inspection) Testing & Maintenance .
Inthis Respect . connections should be in a locationwhere they can reasonably be reached & where there is adequate workingspace . :svengo:
Whereconnections are made in roof spaces & inter-floor spaces the Enclosures containingthe connections should normally be fixed & provision must be made for theiraccess .
Providing )- These TWO CONSTRANINTS are COMPLIED with .Then the continued use of standard circular junction boxes remain ACCEPTABLE . :iagree:
BS-7671 is a British Standard for the “ Requirements for ElectricalInstallations “ it is important torealise that the regulations apply to the “ Design . Erection &Verification of Electrical Installations “
&are NOT intended to be a ( Product Standard ) This is covered at the beginning of thisdocument in Part 1 . Scope :welcome:
Regulation. 113 . Equipment . 113.1. The regulations apply to items of electricalequipment only so far as ( selection& application of the equipment inthe installation are concerned . The regulations DoNot Deal with requirementsfor the construction of assemblies of electrical equipment which are required tocomply with appropriate Standards .
Itis also important to appreciate that BS-7671 does NOTPRECLUDE the use of equipmentthat complies with the appropriate ( Product Standard) regardless of whether the construction of the equipment meets all theRegulations within BS-7671 .
Example.. Etc . CeilingRose . BS-67 . Etc
Abovehave features which are NOT in accordwith BS-7671 but are ( PERMITTED )by virtue of their compliance to the appropriate ( PRODUCT STANDARD )
Is concerned with ( Ensuring ) thatpersons opening the box do not come into contact with ( Live Parts Unintentionally )
412.2.2.3. Where a ( Lid or Door ) inan insulating enclosure can be opened without the use of a tool or key . allconductive parts which are accessible if the lid or door is open shall bebehind an insulating barrier ( Providing a degree of protection not less thanIPXXB or IP2X preventing persons from coming unintentionally into contact with thesesconductive parts . This insulatingbarrier shall be ( Removable only by the use of a Tool orKey )
Regulation relating to Junction Boxes is 521.8.3. p/122 . which requires that where ( Two or More ) circuits are terminated in a Single JunctionBox this shall comply with BS-EN 60670-22 :gettree:
Regulation relating to Junction Boxes is 521.8.3. p/98 which requires that where( Two or More )circuits are terminated in a Single JunctionBox this shall comply with BS-EN 60670-22or BS-EN 60947-7.
Fig 15A . i) . ii) . iii). the same . iv) taking account of the total floor area being served . ( As a rule of thumb . a limit of 100m2 has been adopted )
iv) taking account of the total floor area being served . (Historically . a limit of 100m2 has beenadopted ) :20:
Table 41.1. – Maximum disconnectiontimes . Table 41.2. – Maximum earthfault loop impedance ( Zs ) for fuses . for 0.4s disconnection time with Uo of 230V. Table 41.3. – Maximum earthfault loop impedance ( Zs ) for circuit breakers with Uo of 230V . Table 41.4. – Maximum earthfault loop impedance ( Zs ) for fuses . for 5s disconnection time with Uo of 230V. Table 41.5. – Maximum earthfault loop impedance ( Zs ) for non-delayed RCDs to BS-EN 61008-1 & BS-EN 61009-1 for Uo of 230V – Regulation 411.5.3.
Regulation 411.5.3. Where an RCD is used for earth faultprotection . the following conditions shall be fulfilled : p/50 Wording
Regulation 411.5.3. Where an RCD is used for fault protection .the following conditions shall be fulfilled : p/57 Wording
Aswith the 17[SUP]th[/SUP] Edition . & First Amendment .
411.5.3. Note 2 : Where (Ra ) is not Known . it may be replaced by ( Zs )
Maximum earth fault loop impedance . ( Zs ) for non-delayed RCDsto BS-EN 61008-1& BS-EN 61009-1. for ( Uo of 230V ◄ ) - Regulation 511.5.3.
With the First Amendment : 41.5. Rated residual operating current ( mA ) 30 : Maximum earth fault loop impedance ( Zs) ( Ohms ) 1667* Rated residual operating current ( mA ) 100 : Maximum earth fault loop impedance ( Zs) ( Ohms ) 500* Rated residual operating current ( mA ) 300 : Maximum earth fault loop impedance ( Zs) ( Ohms ) 167 Rated residual operating current ( mA ) 500 : Maximum earth fault loop impedance ( Zs) ( Ohms ) 100
Aswith the 17[SUP]th[/SUP] Edition . & First Amendment . Note 2 : The Résistance ofthe installation earth electrode should be as low as practicable a Value exceeding ( 200 ) Ohms may not be stable . Refer Regulation 542.2.4.
Whatshould I do if the Manufactures InstallationInstructions for a product ( Conflict ) with the requirements of BS-7671:2008 . or include inappropriate or unnecessary Technical Requirements’
Any Installation Instructions considered tobe Technically Unsound should be ( Queried ) with the Manufacturer & / or referred to the ElectricalContractors registration body for Information .
Howmuch power does the Individual Built in-oven Draw . Individual Built in-oven – No hob . Supplied with a ( 13A Plug ) BS- 1363 .
Specs/ Regulations e.g. 3kW / 3000W . ( Maximum you can get from 13A Fuse ) Current - ( Amps ) Power– ( Watts ) / (Voltage )
Current ( Amps ) 3000 ÷ 230V = ( Current ( Amps ) 13.04 Amps) Uo /230V 13Aplug & Socket . ( Note :- 0.04 of an Amp over would be took up in Diversity as stated in BS-7671:200817[SUP]th[/SUP] Edition. :gettree:
TheDesign of UK Electrical Circuit means that NOT only is every Individual Appliance Protected by a Fuse . ( Protected from Overloading )
BS- 1363 – p/278 . 13A plugs . Socket-outlets . connectionunits & Adaptors . BS- 1362 – p/278 .Specification. for general purpose fuse links for domestic & similar purposes ( Primarily for usein plugs )
BS- 1362 – During normal flow of Electricity . The fuse (Permits ) the power to pass Unobstructed . Duringan Unsafe Overload . A small piece of Metal Melts . stopping the flow ofElectricity .
Definitions Part 2 / p/28. p/25 The same.
( Fuse ) A device which .by the melting of one or more of its specially designed & proportioned components. Opens the circuit in which it is inserted by breaking the current when thisexceeds a given value for a sufficient time . The fuse comprises all the partsthat form the complete device .
( Fuse element ) A part of a fuse designed to MELT when the fuseoperates .