O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer
FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “
For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag
CookerDesign Current Calculations
Thefirst thing you have to do is get Your Head around the Calculations !!
(From a Design point of View ) 2392-10
DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000
(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps
2392-10/ Domestic Installation Oven(s)
Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )
-Controlled via a CookerSwitch with a Socket outlet .
Asa Designer . we’ll have to Apply Diversity ??
Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .
TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)
DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .
Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.
Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’
-So your Work out the Total Power Rating & then calculate the Full Load Current
Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW
I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A
UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )
I= 33.48 x 30 ÷ 100 = 10.04A
Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .
Remember )- Supply Cables Rated to suit DesignCurrent ( Iz )
Continuity of CPC.(1 test ) : r[SUP]1[/SUP] & r[SUP]2 [/SUP].
Dead Test :
Safety Isolation Procedures’ . are required hereprier to Testing ☑
Continuity of CPC.Lighting circuit . having identified the right Circuit Breaker
i) Remove the Lineconductor from the Circuit breaker . Then place it into the Earth bar ( MET ) –Line & Earthtogether
if we look at the Test books some indicate the Link between the top of the Circuit breaker to the Earth bar .
ii) Some indicate the CPCfor that circuit is removed & the Line removed& placed into a connectorblock [ anyone of the will do ] “ Loop “
You must go to the furthest point . & With aTest Instrument low-ohmmeter place it on the Low-ohms scale ( Ω ) The Test isthen taken between the CPC & Line conductor at theCeiling Rose :- in this case a reading of .16Ω that is obtained. proofs continuity of the CPC .
• To proof and theory to the ↔ Consumer Unit breakthe Line conductor go back & take a reading . [ it shows greater than rangeproving continuity was CPC was Testedinitially ]
The PSC { prospective short circuit current }is the maximum available current which can flow in the event of a fault betweenLive conductors { Line – Line } or { Line – Neutral } it iseither directly measuredor if your meterwon’t do direct { Line –Line} then
{ Line – Neutral doubled will suffice }
Line & Neutralcables are ShortedCircuited is called the Prospective Short Circuit Current PSCC .
PSC ↔ ( MCB ) ↔ Protectivedevice must be capable of breaking it Safely ◄ ≈ A.C. Sign .
PFeC { prospective earthfault current } is the maximum fault current between a Liveconductor and earth . { Fault Current is ShortCircuit }
This can measured directly or
by dividing the maximum Line– Earth supply voltage by ( Ze )
PFC {prospective short circuit current } is either the PSCC or PEFC . Whichever isGreater .
By Calculation’s to Obtain PSCC { 230 ÷ by Ze 0.15Ω = 1.53kA } Supply has been connected .
{ 400V ÷ Ze 0.15Ω = 2.6kA }
When we are referring to Design ! Designing for an Installation for Domestic . Design stage – Design purposes.
Broken RingFinal Circuit ? ( As a Tester this is what -&-s arelooking for )
However . We find the Ring to be Broken . the Protective Device couldnot do it’s job as it is rated at 32A & the cable is rated only at 20A .Hence Overloading .
TheRing ? becomes Two Overload Radial . ( From a Tester point of View )
TheRing is a Continuous Loopno matter how it has been designed
p/362)- Appendix 15 ( Informative ↔ telling us )
Ring& Radial circuit arrangements
1) Ring Final Circuit arrangements Regulation– 433.1.
( Informative ↔ telling us )
TheLoad current in any part of the circuit should be ( Unlikely) to exceed for long periods the current carrying capacity of the cable ( Unbroken Ring Final Circuit )
Regulation– 433.1. refers ) This can generally be achieved by .
iv)Taking account of the total floor area being served ( The Regulations aresaying - Rule of Thumb . a Limit of 100m[SUP]2[/SUP][SUP] [/SUP] has been adopted) Ring
Nowif we look at the O.S.G. p/158 . A1 Ring 30 or 32A . 2.5 / 1.5 . – Maximum floorarea served ( m[SUP]2[/SUP] ) 100m[SUP]2 [/SUP]
i)locating socket outlets to provide reasonable sharingof the load around the ring .
Consumer Unit Arrangements . Design Stage .
Part “ M “ requires that reasonable provision be made for people togain Access to a building and use its Facilities .
Prescribes that Switches . Sockets outlets . &“ Other Equipment “needs to be at Appropriate Heights .
Wording → “ Other Equipment“ Consumer Unit . Height of between 0.45m from the floor level Up . 0.⇈ to 0.45m ↳ 0.45m to ↱1.2m from floor level .
2392-10 .
Who is responsible for Inspection & Testing .? The person carrying out the Inspection( YOU )
Remember ? Inspection& Testing . are two different words ( Inspection ) ( Testing )
2392-10 )- Work Near Electricity “ Assessor “
You are doing a ►► Risk Assessment
Introduction to Short Electrical Training :
2391-10 – 2392-10 –
All Dead Testing should have Safety IsolationProcedures’ prier to Testing .
Safety Isolation Procedures’ . are required hereprier to all Testing ☑
All Dead Testingshould have Safety Isolation Procedures’ prier to Testing .
i) Using GS-38 Prove Test Leads .
ii) first thing to do is Isolate the Supply . That is going to beTested . - Take the GS-38 test leads to a known sourceto ensure that theyoperate correctly
“ if they are workingaright “ they go tothe supply that is to be Tested – then Test between Line to Neutral - Line to Earth - Neutral to Earth .
iii) Then the Test Leads are replied to a known source to ensure that they are still Operatingcorrectly .
iv) At this stage you are placing a Locking OFF- device – followed by Signs in the area that is tobe Tested .
Execution:
SinglePole ( 1P )
SinglePole & Neutral ( 1P + N )
DoublePole ( 2P )
ThreePole ( 3P )
ThreePole & Neutral ( 3P+N )
FourPole ( 4P )
ElectricalEndurance : MCB
≥32A .. Over .
≤32A .. Under .
AmbientWorking Temperature ( °C )
Part( 1 ) Sorry am having problemdownloading Amber .
DomesticInstallation )- 2392-10 . “ Electrical Calculations’ “
100A supply . ( Scenario )
ElectricShower 50A : ( Power Circuit )
Cooker– 32A :
RingFinal Circuit ( 1 ) 32A :
RingFinal Circuit ( 2 ) 32A :
ImmersionHeater 16A :
UpstairsLighting 6A :
DownstairsLighting 6A :
Add )- up the requirements ofEach Circuit ( 50A + 32A + 32A + 32A + 16A+ 6A = Total Demand 174A )
►►This is because the CIRCUITS are RARELY LOADED to theirFULL CAPACITY . ◄◄ at the One Time
Apprentices. You are Using the Principle of Diversity
Note )- NOT Total Demand 174A
Shower )- Classed as Instantaneous Water Heater )- O.S.G. Table 1B – p97
Row– ( 5 ) NO DEVIRSITY . Plain English 100%
Apprentices. Only the rated LOAD of the Appliance should BE USED …….. ( NOT the RATING of the PROTECTIVE DEVICE ) ◄◄◄ MCB
Shower[ 10.000 ÷ 230V = 43.47A ] Power Circuit.
Cooker)- As a designer . Would you apply Diversity ( YES )
1x 4 kW – Oven :
2x 1.5kW – Hob/rings :
1x 2kW Hob/ring :
1x 1kW Hob/ring :
1x 2kW – Grill :
Totalpower required = 12kW … 12.000 )
TotalLoad ( Amps ) - 12.000 ÷ 230V = 52A
Itis NOT likely that all of the elements of the Cookerwill be Used at the same time .
Dueto the required cooking times of the food the Oven will be On first . & itwill have reached its required temperature before the Hobs are Used .
[The Cooker will have ( Thermostats & SimmerStats build into it which will Switch ON & OFF to maintain the Cooking Temperatures ]
Asform a Designer point of View ? For aShort periods of time an Overload could Occur ) if all Loads on at the SameTime . Xmas Time .
Regulation133.1.1. – Selection of Electrical Equipment . Every item of equipment shall COMPLY with the appropriate BritishStandard .
RegulationBS-7671:2008 . Suggest that a small Overload isbetween ( 1.25 & 1.45A )
RegulationBS-7671:2008 . Protective Devices have toCOMPLY with certain requirements .
(Table 41.3 – p/49 . MCB / RCBOs ) … RCBOs are – MCB/RCDs in One ) Overload & / or Short Circuit :
BS-EN60898 & BS-EN 61009-1 … Protective Devices must CARRY a CURRRENT of atLEAST ( 1.13 times the device rating for 1 hourwithout operating -
Theymust OPERATE within 1 hour at a Maximumof ( 1.45 times their Rating )
Part( 2 ) Sorry am having problemdownloading
“ UsefulJunk “
Apprentices, The current which causes Operation of the PROTECTIVEDEVICE in the conventional timeis Shown by the Symbol ( I[SUP]2[/SUP] )
Diversitycan now be applied .
RingCircuit(s) – O.S.G. . Table 1B - row 9.. ( Only Applies to Domestic Installations ) 2392-10
Diversityis Calculated at 100% .. for circuit ( 1 ) & 40% for circuit ( 2 ) – Plain English Largest / 100% - Second / 40%
O.S.G.– Table 1B row 9 . Ring ( 1 ) Largest / 100% - 32A
O.S.G.– Table 1B row 9 . Ring ( 2 ) Second / 40% ( by Calculations 40% is 0.4 = )
Nowthe Calculation is ( 32A x 40% = 12.8A ) 32A x 0.4 = 12.8A
PlainEnglish Largest / Second .. ( 32 + 12.8 = 44.8A ) → Total allowance for Ring =44.8A
O.S.G.the hint is in the Name 1B ? Immersion Heaters & Thermostatically controlled Water Heater )- NO Diversity
Atthis Stage I must point out )- O.S.G. 1B– Individual Household Installations ( 2392-10Domestic Installation(s) Top of Page .Look PS. That’s what you are Applying
Apprentices)- Only the Total Load should be Calculated . Immersion Heater … ( 3000 ÷ 230V= 13A )
Note: Domestic / 100A . Single Phase
Lightingcan be Calculated using ( 66% ) of the Total Demand.
Twolighting circuits at 6A = 12A … [ 12 x 66% = 7.92A ]
(MD ) Maximum Demand for your Installation is [ 43.37A – Shower : 32A – Cooker : Ring Circuits – 42.8A : Immersion heater 13A : Lighting 7.92A :
Apprentices?? What is the MaximumDemand used Now ??? 43.37+ 32 + 42.8 + 13 + 7.92 = 139.09A
DomesticInstallation(s) Ring Final Circuits areNOT fully Loaded
DomesticInstallation(s) Shower(s) are used for avery short time .
DomesticInstallation(s) Lights are NOT all on atthe same time . Yeah
DomesticInstallation(s) Cooker is Why diversity can be Used
ExternalEarth Fault Loop Impedance ( Ze )
Thisis the Résistance between Live Conductors & Earth
Remember)- You have Résistance in every Cable .
p/161- 612.11.ProspectiveFault Current .ETC.
Itcan be Obtained by ( Measurement ) ( Enquiry ) (Calculation )
230V/ 400V . protected at the Supply cut-out by Fuses [ BS-1361 type 2 : BS-88-2 : BS-88-6 : ??
( Enquiry )
TTSystem - 21Ω . → Apprentices . O.S.G.- p/11
TN-S - 0.8Ω
TN-C-S– 0.35Ω
Calculationsfor cable size . can be carried out using these values . it is Important toMeasure these values before allowing the Installation to be put into Service .
PLEASE NOTE )- The Only system for which calculation of ( Ze) would be possible is a ( TN-C-S system )
Thisis because the Fault Path External to the Installation is the same for both (PSCC ) & ( PEFC ) - Prospective EarthFault Current
Forthis Calculation to be carried out ( The value of ►► PSCC between Line & Neutral shouldbe Known .
Ohm’sLaw )- Uo / Ze = PSCC .
Symbols’used in the Regulations - p/36
(Uo ) Nominal A.C. rms Line Voltage to Earth ( V )
(Ze ) That part of the Earth Fault Loop Impedance which is External to the Installation . ( Ωs )
HiBruce .
Electricians’.
:19:
Lighting Protective System .Should be considered with regard to Bonding .
Theperson carrying out the WORK has a full Understanding of ( BS-EN 62305 )
2392-10:
BS-7671:2008 . Only provides us with Informationwhich is relevant to Equipment which we could purchase & fit at the time itwas published .
Regulations)- Table 41.3 . Example – BS-EN 60898MCBs . BS-EN 61009-1 – RCBOs
Why?? for us . To use different ProtectiveDevice(s) to be used on Domestic Installation(s) Why ? We have different types of Levels of OVERLOAD .
MCBs- B – C – D .
UsefulJunk
( A ) is NOT used asIDENTIFICATION as it could be CONFUSEDwith the CURRENT RATING of the DEVICE .
No Insulation has ( Infinite Résistance ) is perfect . ( IR ) Insulation Résistance
Youcan get Small Amounts of Electricity flowing along & through Insulation to Ground/ Earth
( IR ) Insulation Résistance
CommonSense tells us that the more Voltage we have .The more Current there’ll be .
TheLower the Résistance of the Cable/ Wire – The more Current for the same Voltage.
Whatmakes Insulation GO bad ? Just one Example .Yeah
:45:
GoodInsulation has High Résistance .
PoorInsulation . relatively Low Résistance .
Dependingupon such factors as the Temperature or Moisture content of the Insulation [ Résistance decreasesin Temperature or Moisture]
Combinedwith the Electrical Stresses that Exist ??
Asa Pin Hole(s) or Crack(s) develop. Moisture &foreign penetrate the surface(s) of the Insulation . ( Providing a Low Résistancepath for Leakage Current )
Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
Good to know thanks, one can never have enough places to source parts from!
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...