O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 ÷ 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
UsefulJunk . ( IR )

Formany years One – Megohm has been Widelyused as a fair allowable lower limit for Insulation Résistance of OrdinaryIndustrial Electrical Equipment
Ratedup to ( 1000 Volts ) PS – Wording Above 500V - 1000V

Regulation. Table 61 – p/158 . Will Reinforce this Matter .
 
Apprentices> When a Measurement of ( PFC ) is taken as Close to the Supply Intake asPossible . ( Meaning !! At the Origin )

Apprentices> The 5 xtimes test must Only be carried out on RCDs with trip ratings ( I∆n ) up to 30mA -&-sQ/As ( Or less 30mA )

Apprentices> Maximum ( Zs ) What is the Measured value of ( Zs ) for anAltered Circuit ? A ) That it is Lowerthan the Maximum Permitted Value .

Designing: Supply Characteristics .
Natureof Supply Parameters [ This can be gained by Enquiry or Measurement ]

U )-Is Line to Line orLine .
Uo)- is Lineto Earth

Symbolsused in the Regulation . p/36 )- U . Voltage betweenLines . ( V )
Uo)- is Lineto Earth ( V )
 
Electricityonly has Current when it is on the move . Yeah .

Formulafor Inductive Reactance : XL = 2πƒL

Thereare 4-factors thatdetermine the Résistance of a material :

1)Type of material :
Therésistance of various types of materials are different . for instance . gold isa better conductor of electricity than copper . & therefore has lessrésistance .

2)Length :
Therésistance of a material is directly proportional to it’s length . The longerthe material is . the more résistance it has . This is because the electronsmust flow through more material . & therefore meets more friction over theentire distance .

3)Cross-Sectional Area :
Therésistance of a material is inversely proportional to the cross sectional areaof the material . This means that the thicker the substance is across . thelower the résistance .
Thisis because the larger the cross sectional area is . the less friction there isover a given length [ picture in your mind . if you will . that a fire hosewill pass more water than a garden hose . because the wider the pipe . the lessrésistance it has ]

4)Temperature :
Invarious types of materials . résistance can vary inversely or directly with thetemperature . This is because of the chemical properties of the material . incarbon . for instance . the résistance decreases as the temperature rises . Sowe say it varies inversely . in copper . however . the opposite is true . withthe rise in temperature . we have a rise in the résistance .

* So not only can résistancechange with heat . but causes heat as well .
 
Regulation705.512.2. External Influences :

( Agricultural & HorticulturalPremises)

Callsfor all equipment to have a degree of Ingress Protection of at least ( IP44 ) for protection against water splashing from any direction .
Wheremore Onerous Environmental Conditions Apply ?? Higher degree of IngressProtection will be required .

Compliance: Regulation 705.512.2. )- Where equipment of ( IP44) rating is NOT available . it shall be placedin an EnclosureComplyingwith ( IP44 ) ◄◄

IPX5)- Protection against Water Jets from anydirection ( Note : Under stated conditions )
IPX6)- Protection against Powerful Water Jets fromany direction
IPX7)- Protection against the effects of TemporaryImmersion in Water .
IPX8)- Protection against the effects of Continuous Immersionin Water .

:party:
 
Apprentices& 2392-10 )- Please take the Time to Read
:24:

This Test is Conducted on Domestic Installations .

I do this Test First . Why ??To make sure that I have a Earth returning back to Transformer Windings . External
BeforeI connect up My Earthing to the Consumer Unit.

TestSequence & Descriptions .

Thefollowing Test(s) are carried out with the SupplySwitchedOFF
ExternalEarth Fault Loop Impedance . ( Ze )

TheReason behind this Method )- To establish that a good Earth Exists at the Installation in Order for theremaining Test(s) to go ahead.
ProspectiveFault Current . ( PFC )

612.11.)- Protective EarthFault Current shall be Measured .
Bydoing this Test you have to Remove (Disconnect the Main Protective Bonding Conductor ) Earth – from the ( MET ) in the Consumer Unit . ( METMainEarthing Terminal)

TheReason behind this Method )- You are Removing Parallel Earth Paths . ◄◄◄◄
ByTesting the Line & Earth. You have a straight path to back to the Transformer Windings .

(Ze ) Measured at the Supply Position .

Onelead on ( The Disconnect the Main Protective BondingConductor ) Earth
&the Other Lead on ( At the Top of Main Switch ) Line

Younow have a Closed Circuit . ( Protective Earth Fault Current shall be Measured )

Itis one off the Easiest of all Test(s)


Line & Earth cable Only which has been Removed from ( MET ) Simple -&-s will pick your Brains on this ◄ 2392-10

-&-s)- The following Test(s) are carried out with the SupplySwitchedOFF

Apprentices( What is Ze I hear you Say ??? )
Symbolsused in the Regulation . p/36 .
Thatpart of the Earth Fault Loop Impedance whichis External to the Installation ( Ωs )
 
Apprentices: Basics
Rememberthat the : 17[SUP]th[/SUP] Edition – is British Standard :iagree:

Meaning)- ( R1 +R2 ) …. Line / R1

Meaning)- ( R1 + R2) …. CPC / R2

Putthe two together . You have ( Line / CPC ) ↔ ( Line - R1 + CPC - R2 )

Inany Exam . The Regulations will get you out of Trouble .

Toconfirm This .

Symbolsused in the Regulations p/36
( R1 ) – Résistance of the Line Conductorof a Distribution or Final Circuit (Unit )
TheRegulations are pointing you to . Appx 4 – Schedule of Test Results .

Symbolsused in the Regulations p/36
( R2 ) – Résistance of the CircuitProtective Conductor( CPC )of a Distribution or Final Circuit ( Unit )
TheRegulations are pointing you to . Appx 4 – Schedule of Test Results .

(Ze ) External to the Installation p/36
Meaning )- Outside of theBuilding → Ze ] ↔ [ Zs Inside of Building.

(Ze ) You are checking that you have agood Earth from the Transformers Winding
(Zs ) You are checking That your Installationis Earthed (Zs ) 612.9 – The Earth Fault Loop Impedance . is required to be determined forthe furthest point of each circuit

-&-s You will be asked the Qs ) Formula Calculating Earth Loop Impedance . itwill be the Option of 4 Qs ) mixed up .
( Zs = Ze + R1 + R2) ◄◄ This Qs is the start of Testing Calculation(s) for 2392-10

The colour has been added for Clarity
 
ApprenticesBasics
LearningCurve

Regulation(s)p/333

( EIC ) Electrical Installation Certificate

Weare looking under ( Main Protective Conductors )

EarthingConductor : - Material( Copper ) C.S.A ( 10mm[SUP]2[/SUP] ) … Connection Verified Tick inbox
MainProtective Bonding Conductors : - Material (Copper ) C.S.A ( 16mm[SUP]2[/SUP] ) … Connection Verified Tick inbox

Youare Confirming )- To incoming Water & / or Gas service … ConnectionVerified Tick inbox

TheEarthing is very Important in any Installation/ or Jobs

Pointto Note : Please mark your Earthing in ConsumerUnit ?? Gas / Water ( White InsulatingTape . Why ?? if you have to come backfor any Reason you can Indentify for Testing reason . Testing comes under Common Sense . Yeah

Remember that the Certificationis you Proof in a court of Law i) Your complied with British Standards . ii)As a Competent Person . Tester .
:35:
 
Testing. Yes this will come up on 2392-10 -&-s Q/As

Initial VerificationNew Installation ( Certificate )
Regulation632.4.
All)- defects or omissions revealed during Inspection & Testing of theInstallation work covered by the ( Certificate ) shallbe made good before the Certificate is issued

PlainEnglish : The regulation(s) are telling you to Cover you But .
Electricians’are not Perfect 99.9% . mistakes can bemade accidently . The Reason for Testingin Order from the Regulation(s) is that every test has a reason(s) ??

TheRegulation(s) prescribed Tests . Etc

612.2.1.Continuity of ProtectiveConductors ( Dead Test) Do we have Earthing ?? ETC .
612.2.2.Continuity of Ring Final Circuit Conductor( Dead Test ) is the Ring a Complete Loop?? ETC . Do we have reverse Polarity
612.3.2.Insulation Résistance ( Dead Test ) has the cable been damaged ?? L/N – E . Megger 1552 two leads .

500V≥ 1.0MΩ ( Mains ) 2 x 230V = 460 / 500V ( your fire up doublethe Voltage ) Testing the Cable only
SELV: = 50V .A.C. = 250V D.C. ≥ 0.5MΩ
(They are only three Qs on this matter ( Table 61 – p/158 – ( 250V ≥ 0.5MΩ ) ( 500V ≥ 1.0MΩ ) ( above 500V – 1000 ≥ 1.0MΩ )
Look at the Wording . SELV / (250V ≥ 0.5MΩ )

2392-10)- Testing Q/As -&-s Yes ◄
612.3.3.Where the circuit includes ELECTRONICE DEVICESwhich are LIKELY to INFLUENCEthe results or be DAMAGED.
Onlya MEASUREMENT between the LINE conductors connected together & the EARTHING ARRANGEMENT shall be MADE . ( L& E ) Only

Nowthe Regulations are TELLING us ????? ( CoverourButs )
NOTE 1 )- AdditionalPrecautions . such as ( DISCONNECTION ) may be NECESSARY to avoid damage to ELECTRONICEDEVICES

Nowwe can say Informative
 
Apprentice’sBasics .

Continuityof Protective Conductors . 612.2.1.

Method 1 )- ( R1 + R2 ) Line / CPCThis also proves Polarity
Method 2)- ( Measurement of R2 → or Bonding ) R2 / Wander Lead

Point to Note )- Test Voltages & Minimum Insulation Résistance .
Table 61 – p/158 - 500V to 1000V ( Above )

613.3.1. Insulation Résistance ( Domestic Installation - 500V between Live conductor(s)where appropriate during this measurement . Line & Neutral may be connected together . L/N –E separate
 
RingFinal Circuit ( DeadTest ) Loop Testing

Thereason behind this Test !!
RingLoop Testing ensures that any Ring Circuits wired in the Installation you havecreated are actually a ( RING CIRCUIT ) & not forming a ( Radial )
Figure of Eight loop

Testing must include the relevantTests from the following Checklist ( 612. )

O.S.G.(- When a Test shows a failure to comply . The installation must be corrected .The test must then be Repeated . As must any earlier test could have beeninfluenced by the failure .

Itthen chases onto the Regulation(s) 612.1.
TheTests of regulation(s) 612.2. to 612.13. where relevant . Shall be carried out &the results compared with relevant Criteria .
TheRegulation are telling us in Order . each test has its Reason

Apprentices. O.S.G. p/80 – 2392-10 will use this system

Continuityof Ring Final Circuit Conductors . p/80 – A Three-step Test is required to Verify the Continuity of the Line . Neutral & Protective conductors & the correct wiring ofthe Ring Final Circuit . Etc

Step1 )- p/81 / End to End ( MeasuredSeparately ) L/N/CPC
Step2 )- p/81
Step3 )- p/82

Youwill see ?? ( Little r[SUP]1[/SUP]+ r[SUP]2[/SUP] ) don’t get confused with ( R1 + R2 )
 
2392-10: NEW
Purposeof Initial Verification .

InitialVerification . in the context of Regulation 610.1.is intended to confirm that the Installation complies with the Design & hasbeen Designed & constructed in Accordance .
610.1. ) 611.2. ) 612.1. )
 
2392-10: ( T )
Certificates

Appendix6 of BS-7671 contains Three model forms for the Initial Certification of a ( NEW ) Installation or for an Alteration or Addition toan existing installation as follows.

Ambringing you to the Point )- Single Signature ( ElectricalInstallation Certificate)- That is you 2392-10
WhereDesign . Construction . Inspection & Testing are the RESPONSIBLY of ONE PERSON )- That is you 2392-10

ACertificate with a Single Signature MAY REPLACEthe MULTIPLE SIGNATURE form ◄◄◄
:iagree:
 
2392-10: This will come up -&-s
:sweatdrop:
Regulationp/339 . ( PIR)

Periodic Inspection Report .
Regulations )- row 5 . The “ Extent& Limitations “ box should fullyIndentify the elements of the Installation that are covered by the report &those that are not . This aspect having been agreed with the CLIENT & other interested parties before the Inspection & Testingis CARRIED OUT .

Tester. GN-3 p/19 .
Scope)- it is essential that the Inspector & the Person ordering the Inspectionknown the “ Extent “ of the Installation to beInspected & any Criteria regarding the “ Limit“ of the Inspection . ( BOTH should be AGREED & RECORDEDon the CERTIFICATE )

Regulation)- Schedule of Inspections P/340
Bottomof Page ??

NOTES : ( LIM ) ◄◄ -&-s/ Big time . PS trip up Q .
ToIndicate that . exceptionally . a “ LIMITATION“ agreed with the person ordering the work preventedthe Inspection being carried out ( Applicable for a PeriodicInspection Only )
 
2392-10: ( ADS )
:iagree:
TestingRCDs
Wherean RCD has a rated value of ( I∆n ) not exceeding ( 30mA ) & is used toprovide Additional Protection to BASIC PROTECTION the operating time of the device mustnot exceed ( 40mS ) when subject to a Test Current of ( 5 x I∆n )
 

Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top