Hi All

I’m presuming a standard pendant is a class 2 fitting as the earth terminals are not needed as it’s a plastic fitting and it only has an insulated 2 core going to the actual ‘lamp part’.

Am I correct in thinking this?

The reason I ask is Screwfix have replied to someone’s question that it is a class 1 and requires an earth? Even though it is only used to loop in/out.

Can anyone clarify this for me.

Thanks E4F9170E-4F95-44C1-B671-7ACCE8B5BBFF.jpegA7B978CF-7918-4E13-8D37-39AFE2E772C6.jpeg
 
Absolutely, but as in this instant the new build shower did not want to spend the money on an enclosed light fitting, so that stick a celling mounted batten holder up, IMO the angled would have been better.

This house had a bulhead fitted under the stairs - far from ideal, but little chance of a broken lamp leaving live parts exposed. Probably would have cost any extra to fit a more suitable surface mounted light.
 
It's not actually near any combustible surface though, and will be 'F' rated for the surface it's screwed to. It's just inside the door frame, and well away from the back wall, but really sticks out into the door aperture. Much worse than it looks in my pic.
 
It's not actually near any combustible surface though, and will be 'F' rated for the surface it's screwed to. It's just inside the door frame, and well away from the back wall, but really sticks out into the door aperture. Much worse than it looks in my pic.
The architrave & door are combustible surfaces, and certainly nearer than 500mm. They don't really like it being nearer than 600mm.
 
I see what you mean, but the days of 150W incandescent lamps are hopefully over. If there's any danger from heat from that lamp, it'll be when the cupboard gets stuffed full, and the lamp accidently ,or deliberately, becomes a peg for hanging something flammable on.
If you saw it in the flesh, I think most of you would agree that the biggest danger is from when (not if) it gets broken off.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Wales
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Is a standard Pendant a Class 2 fitting?
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
66
Unsolved
--

Advert

Thread statistics

Created
bilabonic,
Last reply from
Risteard,
Replies
66
Views
9,554

Advert

Back
Top