OSG appendix H4 seems to ask for a switch not more than 2m away.
Unless I'm mis-reading it.

remember that the osg is just a guide. bs7671 doesn't really make reference to the 2m rule - not the current edition anyway. bit daft, i know, but that's the iet for you. as long as section 537 of the reg's is being observed, the installation isn't breaking any rules. table 53.4 shows that an mcb can be used for isolation, functional and emergency switching.
 
The regs are minimum standards, sometimes common sence and professional practice overides them, I'd sack anyone installing a cooker circuit and not a double pole isolator near it for isolation in a domestic situation
 
The regs are minimum standards, sometimes common sence and professional practice overides them, I'd sack anyone installing a cooker circuit and not a double pole isolator near it for isolation in a domestic situation

i'm with you mate. sadly, common sense and professionalism are rare commodities in this day and age.
 
I think the osg guidance on this is a hybrid of BS7671 and building regs if I remember correctly, which TBH I probably don't :)

that oven must be a commercial one then.
 
Functional control


This control relates to all switching operations in normal service conditions for energizing or de-energizing a part of a system or installation, or an individual piece of equipment, item of plant, etc.
Switchgear intended for such duty must be installed at least:
At the origin of any installation
At the final load circuit or circuits (one switch may control several loads)
Marking (of the circuits being controlled) must be clear and unambiguous.
In order to provide the maximum flexibility and continuity of operation, particularly where the switching device also constitutes the protection (e.g. a circuit-breaker or switch-fuse) it is preferable to include a switch at each level of distribution, i.e. on each outgoing way of all distribution and subdistribution boards.
The manœuvre may be:
Either manual (by means of an operating lever on the switch) or
Electric, by push-button on the switch or at a remote location (load-shedding and reconnection, for example)
These switches operate instantaneously (i.e. with no deliberate delay), and those that provide protection are invariably omni-polar(1).
The main circuit-breaker for the entire installation, as well as any circuit-breakers used for change-over (from one source to another) must be omni-polar units.

onni polar means disconnects All poles
 
I was actually hoping people would read rather then having to explain simple things like functional switching!

that wasn't being bitchy btw just defending my laziness
 
Last edited by a moderator:
quoting chunks of the regs is easy.
I would much prefer to see your own interpretation of them.
Then people like me can learn from you.
 
Ok mate,
The regs state that cooker circuits must have functional switching (cooker switch) the on site guide then backs this up by saying that a cooker switch must be located within 2 metres of the appliance. It's not only the regs that you do it for there is also the practical reasons (you can't reset that bloody alarm I sometimes set by leaning on the cooker) and also testing.

I've only just finished college so I read up as much as I can and usually just scroll around the forum picking up information from new posts. I'm sure I take in information incorrectly sometimes so it's good to be tested on it!

btw that was 4 years of college not 5 weeks
 

Reply to isolation required?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
224
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Terminal box on a UK cooker from 50 years ago would easily accomodate a 10mm2 cable, even though 6mm 2 was adequate. Nowadays, most cookers, ovens...
Replies
4
Views
310
Sad as it is I have to say it, but 'twas ever thus, and where they're concerned predates scheme requirements. On first contact they take a rather...
Replies
67
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top