Im sure this has probably been asked before in this forum but ive just upgraded a fuseboard today and found no earth in the lighting (two core). Obviously the next thing to do would be to tell the customer either rewire or change everything on that circuit to class 2 fittings and accessories, but in this case the customer didnt want to go ahead with either.... what should i do? Cutting the circuit out would be abit extreme?
 
On the initial site visit for the estimate drop off one switch, check for bonding etc.. On the day carry out your tests before removing the old fuse-box and probe all metal fittings with the wander lead. If you get any dubious readings or low IRs bring to the customer's attention before commencing. Have a separate price for the testing on the estimate and if necessary walk.
So charge them for taking a few R2’s and if there not happy then dont do the job? How much are you charging for the “pre fuseboard” checks?
 
Before removing the old fuse box I carry out RFC continuity, protective conductor continuity, IR, Ze and Zs.If there is no continuity I will allow an hour for some basic fault finding too. I dont want to loose a days money by walking but at the same time I dont want the client phoning me at 2am to say the RCD keeps tripping. Read Electrical Safety best practice guide.
 
doing a cu change on tuesday....went there yesterday to have A LOOK......removed a few switches up and down...removed a few light fittings and roses up and down.....no c.p.c.....took half an hour...where is the problem in a few simple checks before you change the board
 
The guidance all state that we should rectify a dangerous circuit before reconnecting to a new CU.
However you have made the installation safer as you have provided additional RCD protection, if it were to go to court you could argue this, and you would have a strong case.
I would offer to fit class 2 fittings for free, if the customer does not go for this then I would write a letter explaining the dangers and get a signature.
 
How many light fittings are you talking about?
Legally you cant cut the lighting circuit out as we dont have the same powers as Gas Safe. All you can do is explain the dangers to the client and offer to replace the fittings with plastic pendants or similar for no charge.
I cant see how you can provide an EIC with all the tick boxes on the inspection section.
 
If you changed my cu and then tried to get me to sign anything saying it was dangerous, I’d tell you to whistle.
Well it's the situation the OP has put themself in.
It is safer than it was, it now has RCD protection, although he shouldnt have connected this into the new CU, there is always that argument against a non-statuary document.
 
I assume from the info this is domestic and hence the EAWR 1989 do not apply if they did you have no defence in a court of law as provision for earthing is an absolute regulation. The argument rcd protection has made it safer is a weak argument as you cannot rely on such a device due to the absence of an earth because the requirements of ADS are not met.
 

Reply to No earth in lighting circuit what next? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hello Brianmoooore, Thanks for yor reply - Sorry that I did not see your message until today - the Forum replies notification emails about your...
Replies
7
Views
670
Ok I’ll try this when I’m down
Replies
4
Views
395

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top