IEC-479-1 :
A residual-current-device . will ( Reduce ) the risk of Electric-shock .
Providedit has a residual-operating-current . not exceeding 30mA. & an operating-time not exceeding. 40mS . when a residual-current of 150mA - flows .
Thesecharacteristics are derived from the graph-shown . effects of current on thehuman-body can tolerate verysmall-currents for reasonably-long-periods . & moderate-currents forvery-short-periods .
Conductor(s): résistance .
Theease by which a . material-conducts electricity . is known as - résistance .
Conductor(s)- Interpreting .
Neutral-conductor. is defined as a . Live-conductor .
p.31: Neutral-conductor - A conductor connected to the . neutral-point of a system .& ( Contributing ) tothe transmission of ( Electrical-energy )
p.30: definition of - Live-conductor . refersto the . definition for . Live-parts .
Live-parts- a conductor or conductive-part intended to be . energized innormal-use . ( Including ) a neutral-conductor . Etc . This confirms that the . Line &Neutral-conductors . are both . Live-conductor(s) when energised .
(G ) RCD - device . as the earth-fault-current - ( If ) is . likely to be much higher than the . IΔn settings of the device installed . 30mA ÷ 1000 = 0.03A .
2394:
Circuit-breakers. ( is both a Circuit-breaking-device ) Emergency / switching . Table - 53.4.
Overcurrents- are detected by . three-different-devices .
-Thermal for Overloads .
-Magnetic releases . which aregenerally-combined - ( Thermal / Magnetic-circuit-breakers )
2394: Very basics . BS-EN-60898 - Manual or Automatic-control - of acircuit .
Circuit-breakersare identified with . Two-breaking-capacities .
6kA )- . BS-EN-60898- standard for household or similar-applications. where Unqualified-persons. can re-closes a circuit with a persistent fault-several-times . the breaking-capacity - in Amps .
p.285 . BS-EN-60898- 1 .Specification for circuit-breakers for . Overcurrent-protection . for household & similar-installations.
p.286. BS-EN-60947-2 . Circuit-breakers 10kA . Qualified-persons .
p.149. Circuit-breakers : Table-53.4.
BS-EN-60898 .
BS-EN-60947-2.
BS-EN-61009-1.
Donot get mix up .
BS-EN-60947 . Low-voltage . switchgear & control-gear .
BS-EN-60947-2. Circuit-breakers - 2006 .
Table- 41.2. : 41.4 : Type of fuses .
Fusesare indentified by . 2 - letters . according to their application-category . in ( LV-installation )
Thefirst-letter . indicates the . main-operation . ( g ) = general .
Thesecond-letter . indicates the . categoryof equipment to be protected .
G) protection of cables & conductors.
M) protection of . motor-circuits .
(gG ) - ( gM )
DNO: It is noted that .Supply-cut-out-fuses . are allowed to be utilized for overload-protection . ofthe main-supply-cables - 433.3.1.
Note : we are using thecircuit-breaker-side BS-EN-61009-1 .
Note : Regulations - 41.3. BS-EN-60898 & BS-EN-61009-1 .
Maximum-earth-fault-loop-impedance. ( Zs ) for circuit-breakers with . Uoof 230V . for . ( Instantaneous-operation ) Etc .
Domestic-installationsthe . ( PFC ) is unlikely to exceed . 6kA . up to which value the . [ Icn ] & [ Ics ] valuesare the same .
PlainEnglish - Note . Two-rated-short-circuit-ratings. protective-devices . BS-EN-60898 & BS-EN-61009-1 .
GN-3: p.100 - reminds us . Generic Scheduleof Test Results .
3). BS ( EN ) enter the . standard of manufacture of the .circuit-protective-device . e.g.
4). Type - where relevant for . circuit-breakers enter the sensitivity type .e.g. - C . ( B . C. D . time-characteristics )
5). Rating - enter the .protective-device-current-rating .
6). Breaking-capacity - enter the . protective-device-breaking-capacity . often “printed on the circuit-breakers “ e.g. 6.
GN-3- p.56 . [ Icn ] & [ Ics ] Two-rated-short-circuit-ratings. table - 2.8. [ Icn - 6 ] & [ Ics -6.0 ]
BS-EN-60898 & BS-EN-61009-1 .
[ Icn ] - is themaximum-fault-current . the device can interrupt safely . …….. [ Icn ] value is normally marked on the device [ 6000 ]
[ Ics ] - is the maximum-fault-current . the device caninterrupt safely without loss of . performance .
6). Breaking-capacity - enter the . protective-device-breaking-capacity . often “printed on the circuit-breakers “ e.g. 6.
For- domestic-installations . the ( PFC ) is unlikely to exceed 6kA . up to which value . [ Icn] will equal [ Ics ]
411.4.7.: where a circuit-breaker . Table- 41.3. for the types & ratings . ofovercurrent-devices . listed may be used . instead of calculation .
wherea circuit-breaker - BS-EN-60898 & BS-EN-61009-1 .
2394: our circuits . are . 411.3.2.2. Maximum-disconnection-times . Final-circuits . Notexceeding 32A . [ 0.4s ]
2394: Am making a Point to Note . can’tstress the importance of GN-3 . with Testing& Inspection . “ simplicity at isbest “
GN-3: Ambient-temperature 10°C . 20°C . ( 2394: regulations - 30°C . 70°C )
GN-3: Table - A4 .
Circuit-breakers. Maximum-measured-earth-fault-loop-impedance ( in Ohms ) at ambient-temperature 10°C . where the overcurrent-device is a circuit-breaker .BS-EN-60898 or RCBO to BE-EN-61009-1 .
Ambient-temperature 10°C
GN-3: in comparison .( C ) 6A - 3.09 . 10A - 1.85 .
(B ) 32A - 1.16 ←
Table- A6 : ambient-temperature - correction-factors . 25°C - 1.06 . Cf .
Note. from - 10°C . 0°C . 5°C . 10°C . 20°C . 25°C . 30°C .
Theambient-correction-factor . of Table - A6 is applied to the .earth-fault-loop-impedances . of tables . A1 / A4 if the ambient-temperature is other than . 10°C
GN-3tells us how to do the Calculations .
Ambient-temperature is 25°C . themeasured-earth-fault-loop-impedance . of a circuit-protected by a . 32A type B- circuit-breaker to BS-EN-60898 . should not exceed . 1.16 x 1.06 = 1.23Ω.
GN-3. Do Not Mix up the .ambient-temperature Table . B.2 - 10°C p.121 . Table . B1 - 20°C . p.120
Regulations- 41.3. : ( C ) 6A - 3.83Ω . 10A- 2.30Ω . as you can see . there’s a difference . Yeah
TT-Installations . “ Protective-devices “
Disconnection-timeof ( 0.2s ) for TT- installation hasbeen introduced in the . 17[SUP]th[/SUP] Edition . This makes the use of an . RCD orCircuit-breaker with a . residual-element . virtually-essential .
UsefulJunk . 2394 :
2008:2011:
Asbefore all Appendices are “ Informative “ other than Appendix 1 . which is “ Normative “ .
Appendix1 is requirement & all others are provided for guidance .
2394: Reminder .
By Definition . p.31 . “ Minor-works “
Additions & Alterations to an . installation that do not extendto the . provision of a new-circuit .
2394: Reminder . “ Minor-works “
p.31: - Examples . include the . Addition of socket-outlet : or Lighting-pointsto an ( Existing-circuit ) therelocation of a . light-switch . etc .
2394: - 559.6.1.9.
Part- 5 : p.178 . A Lighting-installation . shall be appropriate-controlled .
Note : See table - 53.4. p.149 .
Forguidance on the selection of (Suitable-protective . Isolation & Switching-devices)
2394: Can we use . Circuit-breaker - BS-EN-60898 .for Isolation . Functional-switching . Emergency--switching .
BS-EN-60898- Yes . (3) Device is suitable for .on-load-isolation . i.e. disconnectionwhilst carrying . Load-current .
UsefulJunk : 41.3.
Maximum( Zs ) for . Circuit-breakers to . BS-EN-60898 - Overcurrent-characteristicsof . RCBO - BS-EN-61009-1 . for. ( Instantaneous-operating ) givencompliance with the . 0.4s & 5s . disconnection-times at . nominal-voltage . (Uo of 230V )
Characteristics- type - B . ( Zs- Ω ) for device of . rated-current . (In ) 46 / In .
Characteristics- type - C . ( Zs- Ω ) for device of . rated-current . (In ) 23 / In .
Characteristics- type - D . ( Zs- Ω ) for device of . rated-current . (In ) 11.5 / In .
Circuit-breaker- BS-3871 . Still in Use. Obsolete to BS-7671:2011: standards
Whatis the . Maximum-value of ( Zs ) at anominal-voltage . Uo - 230V .
Type- 2 . circuit-breaker . BS-3871 . with a rated-current ( In -30A ) Maximum-value of ( Zs -230V ) is [ 32.8 / In = 32.86 / 30 = 1.1Ω ]
41.3: - 3A . 6A . 10 .
[ Type - B - right hand side of table - 41.3 ] making me . 46/ In
Your Example to work to . Scenario !!. Type - B. circuit-breaker . rated-current ( In ) of 8A .
Overcurrent- characteristic of . RCBO . Maximum-value of ( Zs ) - 230V is 46 / In = 46 / 8 = 5.75Ω . [ 46 ÷ 8 = 5.75Ω ]
Maximum( Zs ) circuit-breakers - BS-3871 . Obsolete to BS-7671:2011: standards
for.( Instantaneous-operating ) givencompliance with the . 0.4s & 5s . disconnection-times at . nominal-voltage . (Uo of 230V )
Type- ( Zs - Ω ) for device of rated-current - ( In )
Type- 1 . 57.5 / In .
Type- 2 . 32.86 / In .
Type- 3 . 23 / In .
Type- 4 . 4.6 / In .
Type- B . 46/ In .
Type- C . 23/ In .
Type- D . 11.5/ In .
Example: Basics .
Maximum-Earth-fault-loop-impedance. Overcurrent-protective-device .
(Zs ) can be found using the formula given . in Appendix - 3 - BS-7671: p.295 .Where :- [ Zs = Uo / Ia ]
Uo ) . is the nominal . a.c. - rms .Line-voltage to earth .
Ia) . is the current-causing-operation . of the protective-device within the specified-time. [ 0.4s or 5s ] obtained from the .manufactures-time / current-characteristics. for this particular-device-type & rating .
Example. manufactures-time / current-characteristics . for a 400A - fuse. to BS-88-2 . gives a value of . ( Ia - 2840A ) for a disconnection-time of 5s .
Usingthe above-formula . the maximum-value of ( Zs ) for a disconnection-time - 5s . & a nominal-voltage ( Uo - 230V ) Now - 230V ÷ 2840A = 0.08Ωs .
Fig- 3A1 . p.296 . …. it is worth keeping the BS-7671:2008:
Fuses: 2008 : complying with these - withdrawn-standswill be found in . existing installations . for years to come .
BS-1361 is → BS-88-3 : fuse-system C .
Table- 41.2. - ( 0.4s ) BS-88-3 :
Table- 41.4. - ( 5s ) BS-88-3 :
Question. Maximum ( Zs ) value for . BS-88-3 . in 41.4 - (b) How these . maximum ( Zs ) values are obtained.
411.4.5.- Formula - ( Zs x Ia ≤ Uo )
Where:
Zs) . Earth-fault-loop-impedance in Ωs
Ia) . Current in amps . which causes the protective-device to operate . withinthe time-specified in table - 41.1. or
Ifappropriate . within the . 5s . disconnection-time-specified in . regulation -411.3.2.3. for TN-system(s)
Wherean RCD . is used . the current ( Ia ) isthe rated-residual-operating-current . which provides disconnection . within thetime specified in . table - 41.1. . or
Ifappropriate . within the . 5s . disconnection-time-specified in . regulation -411.3.2.3. for TN- system(s)
Uo) . Nominal-voltage to Earth . in Volts- 230V for standard . a.c. Single-phase & Three-phase-circuit(s)
Uo- 2011 ) Nominal . a.c. rms or d.c.line-voltage to Earth in volts - ( V )
Appendix- 3 :
Thevalue of ( Ia ) can be obtained by reference to the appropriate . time /current-characteristic of theprotective-devices & RCDs inAppendix - of BS-7671:2011:
20A- BS-88-3 fuses .
Assumewe have a . 230V - TN - a.c. system with. overcurrent-protection . provided by 20A - BS-88-3 . for a final-circuit - not exceeding 32A .
41.1.- requires that disconnection of the circuit . takes place within a .maximum-time of ( 0.4s )
Youron Calculations .
Maximum-earth-fault-loop-impedance - ( Zs ) which will ensure that . 20A - BS-33 fuses will . disconnect the circuit. within - 0.4s
411.4.5. shown above . but transpose . it to make . ( Uo the subject . this gives ) Uo . Zs ≤ Ia . Uo = 230V .
Toobtain ( Ia ) Fig - 3A1 . Appendix - 3 . time/ current-characteristic . for BS-88-3 . fuses .
Fig- 3A1 . I can’t draw a line .
3A1. representing the . 20A - fuse givesus the value of current . ( 113A ) mucheasier to use the table at the .top-right of the page . fromthis table we can see . that the value of current which causes . 20A - BS-88-3 . fuse to operate within. 0.4s is ( 113A ) back to your formula . ( Uo. Zs ≤ Ia 230V ) Zs ≤ 113 . Zs ≤ 2.04Ω .
Table- 41.2. (b) Maximum - Zs . 20A - BS-88-3. fuse is 2.04Ω
Maximum- ( Zs ) Table(s) & Appendix - 3 . relationship between . the current required to. operate the protective-device . & the earth-loop-impedance-values .
Reply to Re-take - Useful Information for 2394 : in the Electrical Course Trainees Only area at ElectriciansForums.net
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
Good to know thanks, one can never have enough places to source parts from!
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...