Which is it for you.......


  • Total voters
    72
radials - pro's

1. no consideration needs to be given to balancing of loads across 2 legs
In a domestic situation you can't be sure of what's going to be plugged in where so that's not a consideration; if anything having a 32A ring makes that more flexible. On a radial the highest current using equipment should be plugged in to the nearest point to the CU which makes it more difficult with a radial, while with a ring you have 2 ways back to the CU.

2. Quicker to test
You still have to plug in to each socket. End to end doesn't take long, quick calculation and you can work out what you should be getting at each socket. Anyone who can't wrap their head around ring final testing probably shouldn't be doing the job in the first place.

3. Quicker to install
Again if you're reducing the capacity from 32A to 20A and thereby cutting out the last leg back to the CU this might be true, but it's not a true comparison. 2.5mm is quicker and easier to install than 4mm.

4. More flexible in cable layout to each point
You still need to run 2 cables either way.

5. Easier to add extra points at later date and with fewer restrictions with regards to where you can extend the circuit
You can spur off a ring. If the circuit is properly designed in the first place you shouldn't need to; a 'tree' arrangement would be a nightmare to find faults on.

6. Less chance of cross connections at the CU
Not with T&E, which would most likely be used in a domestic situation. If you're talking about singles you could say that about cross connection with other circuits.

7. Saves on cable when floors of a property dont require 32A of power , eg 2 bed terrace houses.
As I've said, it depends on the layout of the property. You could have one ring for all the sockets (maybe an extra cct for the kitchen) and split the lighting circuits differently.

8. integrity of the original circuit layout is less likely to be abused or altered by homeowner /diyer.
You could say that about any circuit. You can't account for what a DIYer/DIer is going to do after you've left, but an end to end at the EICR should pick this up.

9. Greater current capacity for the equivalent amount of cable used , eg
how have a ring main for the ground floor of a house - remove the midpoint cable and this leaves you with 2* 20amp radials - so you have a net gain of 8A for exactly no more cable.
You could say the ring option is 'over-engineered' which will give you some extra headroom for volt drop. Remember with a ring you're not splitting the circuit into 2 radials (although you have the option at a later date) so you can allow for greater diversity.
10. If the CPC breaks at some point you still have the CPC from the other leg.

11. You have the option at a later date to split the ring to make 2 20A radials for whatever reason.


12. With a ring you can draw a similar current using less ways on the board.

I said I'd add an extra 1 - turns out I found an extra 3!
That said, I'm not against radials, but they need to be used in an appropriate situation and not blindly used because they're 'the modern way of doing things'.

Sorry for the delay in reply - I went to the pub with my mate instead of sitting at home talking shop on the internet, although to be fair he's a spark as well so we did talk shop.
 
No option for 4mm hybrid ring radials? :ihih:

To throw another spanner into the words, the customer probably won't have the installation tested regularly. We've also (accidentally) had entire houses on a single 20a ring with no problems...
 
you'd never catch me running in a 4mm radial, it's harder terminating 4mm as opposed to 2.5.

also, regarding the "well designed/poorly designed rings" , who the hell bothers to plan out a ring? even if you did 5 years later it would have been a waste of time as everything would get moved. I just couldn't imagine it, asking the customer at first fix stage where everything is going to go, they would not have a clue! and even if they did tell you, it would change as everything always does.

i prefer to use a 32A 2.5mm ring for the kitchen, and a 32A 2.5mm ring for the rest of the house if it's a decent size, if not then a 2.5mm 20A radial. but thats generally speaking, every job is different and needs assessed
 
People are just frustrating!
So long as power comes out of the socket the customer doesn’t give a ---- how it got there.
My own view is the radial is gaining popularity because of inexperienced installers. Be they electricians or DI’s (what ever one of them is).
 
Are we talking domestic alone. If so, much prefer rings in the vast number of cases. In commercial kitchens however, 4mm radials come in very useful in some instances. Can't see any problems terminating, I would suggest changing the sockets to those more suitable, if there are.
For the vote, I'll presume domestic.
 
Last edited:
There are always pro's and con's to any method or type of circuit used. At least in the UK you have the choice of installing 2 types of circuits for small power outlets, ...and as such, a professional electrician will utilise both of these types (Ring or Radial) that best suits the power requirements and situation of the installation.

When either of these types of circuits are installed by experienced electricians, they will/should be, designed and installed to the appropriate current regulations and as such, as safe as each other. I'm not really interested in what DIY'ers or other incompetents may or may not subsequently do, that will always be beyond yours, mine, or anyone else's control.

True, a ring circuit requires a much higher competence level to test and fault find, which is probably why most of the fast track wanna-be electricians prefer Radials over Rings, regardless if a radial would be the most suitable circuit for a given situation or Not!! I think someone called the Ring circuit ''Old Fashioned'' Wonder what they would call a Radial circuit then, ....Modern?? ...lol!!!

The only thing that should determine whether a ring or radial circuit is chosen, should be based solely on the most cost effective method to satisfy the design and needs of that circuit. ...Not on unfounded or biased personal preferences!!!

On a final note, ...if Ring circuits are taken off the books, the final effect will be far more reaching than you first imagine. Remember the whole of the wall power accessory catalogue is based on and around the Ring Final Circuit!!!!
 
My pet hate on an I&T is a board full of 16a radial circuits, I'd much rather test a board with 1 or 2 rings, rather then tracing every circuit out to find what it supplys.
think the standard 3 bed house should have 2x rings.

I don't see the argument for harder to wire etc. basically rings are just radials with an extra leg to go back to the board?
They also allow for plenty of capacity if the use chages, i.e. panel heaters etc.

Both types of circuits have their place, but in my book, The ring is still king!
 
People are just frustrating!
So long as power comes out of the socket the customer doesn’t give a ---- how it got there.
My own view is the radial is gaining popularity because of inexperienced installers. Be they electricians or DI’s (what ever one of them is).

Tony I have to disagree we are not inexperienced and we wire radials
 
I bet there are many electricians who don't know how to fully test a ring, and so avoid it if possible. In fact, there have been a few posts on here by practising electricians, asking how to do so.
 
The main objection to the ring final circuit is the time and bother to test (and I don't mean simply testing for continuity of each leg of the ring). Extra work , extra time and I wonder if it's being done properly.
 

Reply to Ring vs Radial in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
D
  • Article
Which truly is the Number 1 Best Tile Adhesive Brand? Since 2007 Tilers Forums started an annual best tile adhesive Poll and sent it out to the...
Replies
0
Views
119
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top