Spur with two sfcu on it | Page 2 | on ElectriciansForums

Discuss Spur with two sfcu on it in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jul 4, 2010
Messages
69
Reaction score
3
Hi all is this ok to run two sfcu like this ?

[ElectriciansForums.net] Spur with two sfcu on it
Or should i run it like this
[ElectriciansForums.net] Spur with two sfcu on it
 
The spur, ie the cable, is not fused. If it was, the fcu would have to be part of the ring. Then again ,we can all nit-pick.
 
Taffy there is nothing wrong with the first one, have a look at Appendix 15 in the regs book page 425.
The light switch and boiler are both SFCU with 3amp fuse fitted according to the picture.
 
Hi all right the socket is on a ring final then going to the 1st sfcu then looping out to the 2nd sfcu o know you can only have 1 socket off a spur but both sfcu will be at 3a so i don't think i need a sfcu by the socket.
 
Sorry Taffy you lost me on that one i don't see any difference at all Appendix 15 shows spur protecting sockets? You dont need a FCU protecting a FCU where would it end?

Ok, the part of the diagram on page 425 shows a spur off the ring main at 9 oclock. The 13A FCU is limiting the current that can flow through to 13A therefore protecting the cable. The OP diagram 1 shows a spur going straight to the first FCU and then on to another FCU. Therefore with 13A fuses put in each it is possible that the total draw could be 26 Amps thus overloading the cable. The 3 amp fuses fitted to the FCU`s are irrelevant as they are protecting the cable going out from the FCU to the appliance.

Now I appreciate that 6 amps, or the load from a boiler and a light (which is going to be less in all likleyhood) is not going to damage the supply cable however the light and the boiler are " fixed equipment" therefore the relevant part of the diagram is at 6 oclock where only 1 fixed item is allowed.

The reasoning for this reg IMHO is that should the fixed equipment be changed in the future, say an immersion for a boiler and a socket for the FCU running the light then you have an overloaded cable.

I refer to my previous post regarding fixed equipment on spurs.
 
Ok, the part of the diagram on page 425 shows a spur off the ring main at 9 oclock. The 13A FCU is limiting the current that can flow through to 13A therefore protecting the cable. The OP diagram 1 shows a spur going straight to the first FCU and then on to another FCU. Therefore with 13A fuses put in each it is possible that the total draw could be 26 Amps thus overloading the cable. The 3 amp fuses fitted to the FCU`s are irrelevant as they are protecting the cable going out from the FCU to the appliance.

Now I appreciate that 6 amps, or the load from a boiler and a light (which is going to be less in all likleyhood) is not going to damage the supply cable however the light and the boiler are " fixed equipment" therefore the relevant part of the diagram is at 6 oclock where only 1 fixed item is allowed.

The reasoning for this reg IMHO is that should the fixed equipment be changed in the future, say an immersion for a boiler and a socket for the FCU running the light then you have an overloaded cable.

I refer to my previous post regarding fixed equipment on spurs.

I actually think this is an interesting debate and it has got me thinking TBH. I think Taffy is right here. The 13 amp FCU protects the whole of this spur cable in the future no matter what DIY Dan adds to it (and he will). The FCU's downstream could allow 26 amps to be pulled through and damage the spur cable upstream. Hmm
 
Last edited by a moderator:

Reply to Spur with two sfcu on it in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

J
The rcd spur being fitted is probably because there wasn't rcd protection of that supply.
Replies
5
Views
430
Many thanks. Very clear!
Replies
2
Views
192

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top