***Cont../ Useful Information for Electricians & Apprentices***
A
amberleaf
O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer
FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “
For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag
CookerDesign Current Calculations
Thefirst thing you have to do is get Your Head around the Calculations !!
(From a Design point of View ) 2392-10
DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000
(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps
2392-10/ Domestic Installation Oven(s)
Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )
-Controlled via a CookerSwitch with a Socket outlet .
Asa Designer . we’ll have to Apply Diversity ??
Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .
TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)
DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .
Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.
Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’
-So your Work out the Total Power Rating & then calculate the Full Load Current
Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW
I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A
UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )
I= 33.48 x 30 ÷ 100 = 10.04A
Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .
Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
Electric Shock : FaultProtection
The term “ Fault Protection “ is used in BS-7671:2008 .to refer to protection of persons & livestock against Electric Shock as aresult of making contact with Exposed-conductive-parts that have become LiveUnder Fault Conditions . ( mainly with regard to failure of basic insulation )
Definitions – p/24. FaultProtection : Protection against electric shock UnderSingle-Fault Conditions .
• Preventing a current resulting from a fault frompassing through the body of any person
• Limiting the current which can pass through the bodyto a Non- hazardous value .
• Limiting the duration of a current resulting from aFault which can pass through the body to a Non- hazardous time period .
Regulation . 131.2.2. ( goes onto Confirm that )
In connection with Faultprotection . The application of the method of ProtectiveEquipotential Bonding is one of the ImportantPrinciples of Safety . ◄◄
:thinking2:
SP&N . single-pole & neutral .
TP&N . triple-pole & neutral .
2392-10 : Design .
:oops:
Section 133 of BS-7671:2008 Containing ( 10 Regulations) . requires equipment to be suitably selected . ?
Erection )- Initial Verification of ElectricalInstallations / & Periodic Inspection & Testing .
The requirements for erection & Initial Verificationof electrical installations & those for Periodic Inspection & Testing arecontained in Sections 134 & 135 . Respectively
BS-7671 . The requirement contain in Regulation134.1.1. For Good Workmanship & Proper Materials to be Used .Etc.
BS-7671 : Summary of Section 133of Electrical Equipment .
Regulation . 133 . General – Dealing With ?
133.1.1 . Equipment to ( Comply) with standards unless Agreed Otherwise.
133.1.2.
133.1.3.
133.2. Characteristics’ .
Equipment to have suitable Characteristics to suit theValues & Conditions on which the Design of the Installation is based.
133.2.1. Voltage . These FourRegulations require equipment to be selected to SUIT.Voltage : Current : Frequency & Power :
133.2.2.
133.2.3.
133.2.4.
133.3. Conditions of Installation : Equipment to be selected to be suitable for the Environmental Conditions. or otherwise Protected .
133.4. Prevention of Harmful Effects : ElectricalEquipment not to cause harmful effects on other Equipmentor the Supply .
2392-10 : Design .
:thinking2:
Important Regulation )- 2392-10 . The requirementfor Electrical Equipment to be Installed in Accordance with the ( Instruction(s) Provided by the Manufacturer )
134.1.2.)- Goes on to Require that Equipment must NOTbe IMPARIRED by the INSTALLATION PROCESS .
2392-10 : Design .
:oops:
Summary of Section 134 – Erection & InitialVerification of Electrical Installations . & Section 135 – Periodic Inspection& Testing .
Regulation .
134.1.1. – Good Workmanship & proper Materials .
134.1.2. – Characteristics of equipment Not to be Impaired.
134.1.3. – Conductors to beIndentified .
134.1.4. – Electrical joints& connections to beAdequate .
134.1.5. – Design temperatures NOTto be Exceeded .
134.1.6. – Equipment causing high temperatures or Arcsto be suitably located or guarded .
( T ) 134.1.7. –Suitable warning sigs & / or notices to be provided where necessary forSafety Purposes.
( T ) 134.2.1. – Initial Verification )- Appropriate Inspection & Testing to beperformed during Erection & upon completion of an Installation or an Additionor Alteration . & Appropriate Certification to beIssued .
( T ) 135.1. – PeriodicInspection & Testing )- Recommendation for subsequent Periodic Inspection& Testing required .
2392-10 : Design .
:thinking2:
Whilst “ Maximum Demand “ & Diversity “ are notdefined in BS-7671:2008 .
Following Meanings ..
• Maximum Demand )- The Maximum anticipatedinstallation “ Load “ plus allowance for ( Future LoadingDesigning )◄◄ Potential Load
• Connected Load )- The totalof all Electrical Loads .
• Diversity )- The ratio of Maximum Demand to the ( Connected Load )
Diversity . Therefore can be represented by .
Diversity = Maximum Demand ---- Connected Load.
Diversity )- is never going to be more than ( Unity or 100% )percentage terms .
2392-10 :
:thinking2:
( T )Verification )- Regulation. p/31
All measurements by means of which Compliance ofElectrical Installation with the reverent requirements of BS-7671 . are “Checked “ comprising of Inspection . Testing & Certification
Protection against Electric Shock . ( Making you Aware of it )
:41:
Fundamental Requirements . ( Some times it’s rightunder our Noses )
Part 1 – Chapter 13 . 131.2.1. / 131.2.2.
Protective Measures – Part 4 . Chapter 41 – ( All )
Devices for Fault Protection . – Part 5 . Chapter 53 . –Section . 531 . ( All )
Earthing & Protective Conductors . Part 5 . –chapter 54 – ( All )
Part 7 . – Special installations or locations (Particular Requirements )
Chapter 41 (- Appropriate measures for Protection against Electric Shock ( divided into nine sections ) ◄◄
Section – 410 : Introduction .
Section – 411 : Protective measure : Automatic Disconnectionof Supply . ( ADS )
Section – 412 : Protective measure : Double or Reinforced Insulation.
Section – 413 : Protective measure : Electrical Separation .
Section – 414 : Protective measure : Extra – Low –Voltage . provided by ( SELV or PELV )
Section – 415 : Additional Protection.
Section – 416 : Provisions for BasicProtection .
Section – 417 : Obstacles & Placing out of Reach .
Take you Pick .
Protective Measures that are Generally Permitted .
:thinking2:
Protective Measure :
411 )- ADS
412 )- Double orReinforced Insulation .
413 )- Electrical Separation for the Supply to One Itemof Current – Using – Equipment .
414 )- Extra – Low – Voltage – ( SELV or PELV )
Basic Insulation of Live Parts .
:thinking2:
2392-10 )-
i) T&E – PVC . ( Insulation of Live Conductors )
Basic Insulation of Barriers & Enclosures .
i) Consumer Unit . – Barrier ( Protection from Contactwith Busbar )
ii) Consumer Unit . – it has an Enclosure
Why ?? itprevents Physical & Electrical Contact with LiveParts .
Just a Point to Note here :
Regulation 416.1. calls for Liveparts to be covered by Insulation ( That canOnly be Removed by Destruction ) ◄◄
Would you . ?? Use Sleeveor Tape of Insulating Material is Inadequate ifonly because ( itmay be Removed without Destruction ) ◄◄
2392-10 : Basics .
:oops:
Ring Final Circuit .
The normal requirement relating to Protection againstOverload are relaxed in the case of RingFinal Circuit .
Regulation . 433.1.5.provides a “ deemed to comply “ Status for Protection against Overload wherecertain conditions are a prerequisite .
• The Current – Carrying – Capacity ( Iz ) of the cable must be not less than ( 20A )
• The LoadCurrent in any part of the circuit must be UNLIKELY to Exceed for long Periods the Current – Carrying– Capacity ( Iz ) of the cable
Apprentices: Something(s) to thing about . Yeah .
:thinking2:
Protectionagainst Fault Current .
Fault Current is an Overcurrentcaused by either a Short-Circuit .
- BetweenLine Conductors ) or an EarthFault .
- BetweenLine Conductor & an Exposed –Conductive-Part. or Protective Conductor .
- Faults occur as a result of Insulation Failure .
-Bridging of Conductive-Parts by some Conducting-material
Numberof possible Fault Conditions which needsConsideration .
-Short Circuit Faults between Line & Neutral .
-Short Circuit Faults between Line & Line .
- Earth Faults between Line& Exposed-conductive-parts or Protective Conductor.
ForApprentices . Learning Curve . Only – It startsyou working the Regulations . Designing . ◄
:waving:
Wehave a ( 2.5mm[SUP]2[/SUP]) Twin &Earth thermoplastic ( 70°C ) cable installed inConduit with two-other circuit(s)
TheConduit is clipped direct to a masonry wall but it passes through (100mm ) of thermal insulation at an AmbientTemperature of ( 35°C )
Itis protected by a ( 20A ) BS-EN 60898/ MCB .
Wenow need to reference the rating factors . Grouping ( Cg) is the first [ this can be found intable ( 4C1 / p/268 ) Three circuits Enclosed is ( 0.7.) 0.70
(100mm )► Next is thermal insulation ( Ci ) which is found in table ( p/104 - 52.2. & is 0.78 ) & finally we need ( Ca )
( 35°C ) ► ( Ca )Ambient Temperature . Which is found in table ( p/267 - 4B1 & is 0.94. )
Ourcorrection factors are :
Cg – 0.7.
Ci – 0.78 .
Ca – 0.94 .
4D1A )- Example : you areusing . We know the minimum current rating of the cable has to be ( 20A ) rating of the protective device . & we are protecting the circuit fromOverload .
Asit is enclosed in Conduit but clipped direct wecan use the Method ( C ;) we can use this method because we are using separate factors for Insulation .
Tocalculate the current which a cable can carry under these conditions ( Iz ) we need to select a cable .
ForApprentices / Your trying ( 4.0mm[SUP]2[/SUP]) from - column ( 6) – ( 37A ) x 0.7 x 0.78 x 0.94 = 18.98A – As wehave a ( 20A ) protective device this cable willbe Unsuitable .
ForApprentices / Your trying ( 6.0mm[SUP]2[/SUP]) from - column ( 6) – ( 47A )- which clipped direct carry ( 47A ) before any factors are Applied .
( 47A ) x 0.7 x 0.78 x 0.94 = 24.12A -( Iz ) Apprentices So will this Cable be Fine .
Workingmy way around the Regulations . “ Apprentices “
Classification of External Influence . ( AD1Negligible / IPX0)
Firstly )- Definition – p/24 / Part 2 .
ExternalInfluence (- Any Influence external to an electrical installation which affectsthe design&safe operation of the installation.
TheseExternal Influence are shown by the use of Codewhich has two capital Letters & Numbers .
i)-Your first Letter shows the category of - ExternalInfluence
ii)- External Influence relates to the Numberindicates the Level of the External Influence .The higher the ( Worse Influence )
•the first Letter indicates which category the External Influence .
• Thesecond Letter shows what the External Influence relates to the Number indicates theLevel of the External Influence . The higher theNumber the Worse the Influence .
TheFirst indicates which category the External Influence fallsunder
A ) is Environment ( Wet . Dry. Humid . Dust . Vibration . )
B ) is Utilisation ( How isthe building being Used ? . – What is the capability of the person using thebuilding ?. – Are they ordinary personsor perhaps are they Disabled ? .
-How difficult would be if Required
-Does the building contain materials which could Explode .
C ) is Construction ofbuilding . – ( What is the building constructed from ? ) Will it be likely tomove ?
TheSecond Letter indicates what the External Influence couldbe.
IfYou refer to Appendix 5 . p/318 . Look in theEnvironment section ( Category – A ) You cansee that if the Second Letter was ( K ) itwould refer to Flora ( Plant . Moss & the like )
TheLast digit is a Number & indicates theLevel of the Problem which the External Influence islikely to be .
Example: if we look at an External Influence given aCode of ( AD1 ◄ ) We can see that the Letter ( A ) relates to the Environment. & the Letter ( D ) relates to Water & the final digit ( 1 ) Tells us that the problem likely to be caused by Water is negligible .
Whenwe require further information with regard to this ExternalInfluence . We need to look further into Appendix 5 . When we find ( AD1 ) We can see that it relates to Areas where Weather Protection is Notrequired & that the ( IP rating ) forthe equipment is ( IPX0 ) As the External Influence relates to Waternothing is specified for Dust ( X ) & theLevel of protection against protection against Water is ( 0 ) Which means No Protectionrequired . ►► p/323 – ( AD1Negligible / IPX0 )
Youcan see that ( AD8 ) is where the Equipment islikely to be totally Submersed . such as in a ( SwimmingPool ) The IP rating given as protectionis ( IPX8 ) . X . shows that nothing is specified for Dust& ( 8 ) shows that it must be protectedagainst the effects of ContinuousImmersion in Water.
Indexof Protection Codes is Used throughoutBS-7671:2008 . To identify the Minimum Level of Protection .
“Apprentices “ To Covert back to “ Black “ ◄◄
Scrolldown all – by holding the Left Key down on the Mouse . & let go . it willbe all in Black Highlighted
Goto your top browser right hand corner ( A - Hit the Arrow ▼ . hit the Black Button– Automatic )
Protectionof Conductor(s) in Parallel against Overcurrent .
Toinstall conductor(s) in Parallel . most commonoccurrence is . 2392-10 . Installing Ring Final Circuit .
Byusing Two-conductor(s) which are joined at the Far-End . Your circuit canprovide socket outlet(s) over a greater Area .
Thecurrent can be shared between Two-conductor(s)
Regulation(s)– Appendix 15 p/362 . Informative .
i)Locating sockets outlet(s) to provide reasonable sharing of the Load around the Ring .
ii)Taking account of the Total Floor Area being served – ( 100m[SUP]2[/SUP] )
2392-10. As from your point of View . This will result in a Lower Earth Fault Loop Impedance & Voltage drop. ( Vd )
Regulation(s) 612.14 –Red / Cover BS-7671:2008 .
NOTE )- Verification of voltagedrop is NOT normally required during Initial Verification )
Verificationof voltage drop – GN-3 . ( 3 ) P/57
Regs/ Appendix 12 - Informative . p/358
Apprentices– gives Maximum values of voltage drop for either Lighting or other Usesdepending upon whether the installation is supplied directly from ?
Apprentices– Wording ) LV distribution system ( Domestic Installation(s)◄ . OR from a private LV supply ◄ .
RingFinal Circuit (- protected by a 32A device wired in ( 2.5mm[SUP]2[/SUP]/ 1.5mm[SUP]2 [/SUP]) 70°C thermoplastic . Twin-&-Earth ( 4D5 ) Designing point of View .
2392-10- What’s going for the “ Ring “ → Cables is in Parallel . Your halving theLength & Doubling the Cross Sectional Area . ( C.S.A. )
Example Only : ◄ for calculation purposes only
Wehave a Radial Circuit – Protected by a ( 20A device ) – ( 2.5mm[SUP]2[/SUP]/ 1.5mm[SUP]2[/SUP] )
Oneway to look at this !! Maximum Length of the circuit will be limited by voltage drop which is Limited to a Maximumof ( 5% - 11.5V )◄
Calculatethe Maximum Length of the cable . Transpose / Formula – We normally use forvoltage drop . ( Vd )
mVx A x L --- 1000 = Vd .
Transpose/ this for Length . Vd x 1000 --- A x mV = L
Replacing/ Symbols / Figure . - sum in two parts - ( 11.5 x 1000 = 11500 ) ( 20A x 18mV = 360 ) → 11500 ÷ 360 =31.94m . ( L )
Apprentices- Voltage drop islimited to a Maximum of ( 5% - 11.5V )
5%of 230V = 11.5V … ( 5 x 230V ÷ 100 = 11.5V ) Your Calculation for Power / as theRegs say – Other Uses .
AtRadom - 2.5mm[SUP]2[/SUP] / 4D5-Flat . PVC . cables – 18mV
►Very Basic(s) we’ll leave it at that .
Apprentices. you’ll never get this on Exams .
:waving:
Effectof harmonic currents on a balanced Three-phasesystem . ( The Whys )
Harmonicsare caused by electronic equipment which converts ( 50Hz . a.c. to d.c. ) & then backto . a.c. . at a different frequency .
electronicequipment does not usually have constant Impedance . This is because theimpedance changes due to the constant switching of the electronic componentswithin the equipment .
thisswitching On & Off during part of the waveform results in current beingIntroduced back into the distribution system .
thisis because the Currents are at frequencies other than ( 50 Hz ) it is assumedthat a third harmonic is at ( 150 Hz ) the effect of this is Increased Currentin the Neutral .
whichin certain circumstances will be Higher than the Current in the LineConductor(s)
- Uninterrupted Power Supplies – ( UPS ) **
- Computer Power Unit(s) – ( CPU ) **
-Electronic ballast(s)
- Discharge Lighting . ( florescent . mercury .sodium . ) Etc .
TheCalculation(s) has been sent down on one of the pages.
amberleaf,
Dan,